[Equest-users] Cooling demand is Super High
Nick Caton
ncaton at smithboucher.com
Tue Jun 11 15:16:23 PDT 2013
"Space cooling" demand/consumption as an end-use category is relatively simple to track down. If I'm not mistaken, all kW/kWh figures for "space cooling" will tie back to cooling EIR inputs, and the associated scheduling/capacities, on the airside & waterside of things: DX compressors, heatpumps, and/or chillers.
If you're all packaged DX, that narrows the field nicely ;).
The statement "...XX times to high" suggests you have some target/expected value, which would logically be based (if anything) on system capacity... so that's a sensible place to start. Sounds like those inputs check out? Are there any inadvertent system and/or cooling multipliers in play (other than 1.0)?
Messing with the cooling EIR inputs should have a direct effect on the demand values you are observing. Checking the associated inputs is a natural step to follow.
If the maximum demand hour is very much dominated by the space cooling end-use, that makes me consider carefully reviewing the loads around that time of year, even if the annual unmet hours are within reason. These demand results may possibly be the result of some kind of irregular "spike" caused by a fractional load/occupancy schedule typo.
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Pasha Korber-Gonzalez
Sent: Tuesday, June 11, 2013 4:41 PM
To: Paul Riemer
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Cooling demand is Super High
Thanks for all the responses, so quickly! I've checked my unit capacity inputs--and thus tried an "auto-size" run. The capacities are correct, and very low hours out of throttling range. Unfortunately the space cooling demand (kW) did not move at all.
I've referenced my PS-E report and the highest demand is falling under the "space cooling" end use which I think must be the DX compressor energy demand driving this value?? Please correct me if I am wrong.
I will try adjusting the EIR values and see if that will move the kW values down any...
Thanks so much! Any further thoughts are welcome. If anyone is curious to see my model let me know and I am happy to share it for your viewing/troubleshooting pleasure! :)
Pasha
On Tue, Jun 11, 2013 at 3:36 PM, Paul Riemer <Paul.Riemer at dunhameng.com<mailto:Paul.Riemer at dunhameng.com>> wrote:
Report PS-E for your electric meter(s) will show cooling vs. fan and all other electric end uses for both consumption (kWh) and demand (kW).
Paul Riemer, PE, LEED AP BD+C
DUNHAM
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>] On Behalf Of Steve Jacobs
Sent: Tuesday, June 11, 2013 4:26 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Cooling demand is Super High
You can check to make sure your equipment sizing is reasonable.
On 6/11/2013 2:56 PM, Pasha Korber-Gonzalez wrote:
Hi--does anyone have any suggestions on how to trouble shoot cooling energy demand that is about 5 times too high?
I've looked through my schedules, fans/on/off, etc. My building has packaged rooftops and I can't pinpoint the compressor energy demand versus the fan energy demand.
I've searched the archives and haven't come across any solutions for my model results. My energy consumption for elec & htg is aligned however, just the demand is too high (extremely high...)
Thanks in advance for any insight you can share.
Pasha
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130611/73d274ee/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130611/73d274ee/attachment-0002.jpg>
More information about the Equest-users
mailing list