[Equest-users] Cooling Energy Consumption in Winter

Nick Caton ncaton at smithboucher.com
Wed Jun 12 12:27:24 PDT 2013


Hi Vamshi,

Echoing the discussion so far, we can only guess with as little info as has been provided.  Are you trying to justify the results?  Do you perceive this behavior as a problem or unexpected?  Why?

Is the model exhibiting lots of unmet hours or showing any other signs that the modeled systems aren't operating correctly?

Assuming the model is set up correctly, reasons to expect such behavior may include any combination of:

*         Building is located in a climate where little/no heating is typically required in the winter (I also understand India includes tropical/monsoon climates with persistently warm winter months).

*         Building features substantial internal heat gains (people and equipment loads) leading to year-round cooling

*         Building envelope is very well (or perhaps overly well) insulated, holding internal heat gains in through the winter (and so requiring cooling instead of heating)

*         Building envelope by design invites excessive solar gains in the winter through glazing

*         Scheduling of select cooling equipment (such as a chiller) is forcing it to operate through hours where there is little-to-no demand

*         Buildings with occupied "core" spaces removed from the exterior envelope, and especially those with significant internal gains, should be expected to require year-round cooling where other spaces may require seasonal heating.

This isn't an exhaustive list by any stretch, but what comes to my mind first.  Hope this helps you to better define your problem (if there is one)!

~Nick


[cid:489575314 at 22072009-0ABB]

NICK CATON, P.E.
SENIOR ENGINEER

Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com

From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Sami, Vikram
Sent: Wednesday, June 12, 2013 1:39 PM
To: John Aulbach; vamshi ranga; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Cooling Energy Consumption in Winter

Also - location - India is very generic. India is a large country with different weather patterns and climatic considerations depending on where you are. Depending on the location, and your building, cooling energy in winter might not be surprising.

Vikram Sami
Associate Partner



ZGF ARCHITECTS LLP
T 206.521.3509 E vikram.sami at zgf.com<mailto:vikram.sami at zgf.com>
925 Fourth Avenue, Suite 2400
Seattle, WA 98104


From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of John Aulbach
Sent: Wednesday, June 12, 2013 11:35 AM
To: vamshi ranga; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Cooling Energy Consumption in Winter

Sir:

I believe we will need the .INP.p and .PD2 files. I am unfamiliar with Indian weather patterns.

John R. Aulbach

From: vamshi ranga <vamshiranga at gmail.com<mailto:vamshiranga at gmail.com>>
To: "equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>" <equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>>
Sent: Wednesday, June 12, 2013 8:13 AM
Subject: [Equest-users] Cooling Energy Consumption in Winter

Dear All,

I end up with getting cooling energy consumption in winter months and my heating energy comes negligible.

I am using "Packaged Single Zone system", Location - India. Can anyone tell the reason.

Thanks,
Vamshi.

_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>

________________________________
The contents of this email and any attachments to it contain confidential and/or legally privileged information from Zimmer Gunsul Frasca Architects LLP or its affiliates. If you are not the intended recipient, or an employee or agent responsible for delivering this message to the intended recipient, be aware that any disclosure, copying, distribution, or use of the information contained herein is strictly prohibited. If you received this transmission in error, please contact the sender and destroy the material in its entirety, whether in electronic or hard copy format.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130612/43095803/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130612/43095803/attachment-0002.jpg>


More information about the Equest-users mailing list