[Equest-users] Indoor arena suggestions/tips
Kieu Anh Doan
asandcrab at gmail.com
Fri Mar 1 01:54:35 PST 2013
Dear All,
I'm a beginner for eQuest stimulation. Now I'm starting the software for my
Greenhouse 1200 sf area, 6 ft high. Unfortunately my location is Ho Chi
Minh City, Vietnam that there's no weather data to be put in for use. Could
anyone please help me to start?
Doan Kieu Anh,
Ho Chi Minh City, Vietnam
Cell: +8498 559 1925
On Fri, Mar 1, 2013 at 7:12 AM, Nathan Kegel <nathan.kegel at iesve.com> wrote:
> I don’t think this prevents you from taking credit for natural
> ventilation. It doesn’t say you must provide fans, pumps, diffusers, etc.
> You CAN heat and cool with an open window after all – although cooling is
> the far more common application of natural ventilation. J****
>
> ** **
>
> What you would need is a way to model space temperature and control the
> windows (plus any other devices to mechanically condition the space when
> conditions weren’t favourable for natural ventilation) to maintain the
> comfort range. There are tools that allow you to control windows and HVAC
> systems in this manner – based on space temperature, CO2 level, humidity,
> etc. So assuming your space type and climate are good fits for this
> strategy – you can apply the appropriate software and control “sequences”
> to model a system in accordance with Appendix G – and account for wind
> speed, wind direction, temperatures, moisture, etc. in a fully dynamic
> fashion.****
>
> ** **
>
> While I’ve never attempted to use eQuest for this, I have taken this
> approach successfully with tools that are intended to model these types of
> systems. ****
>
> ** **
>
> [image: Description: IES] <http://www.iesve.com/>****
>
> *Nathan Kegel*
> *Project Manager*
>
> *Business Development Manager* ****
>
> Minneapolis****
>
> T:****
>
> 763 276 9981****
>
> M:****
>
> 415 420 9314****
>
> http://www.iesve.com ****
>
> **Design, Simulate + Innovate with the *<Virtual Environment>*** ****
>
> Integrated Environmental Solutions Limited. Registered in Scotland No.
> SC151456
> Registered Office - Helix Building, West Of Scotland Science Park, Glasgow
> G20 0SP****
>
> Email Disclaimer <http://www.iesve.com/disclaimer.html> ****
>
> ** **
>
> ** **
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Stormy L.
> Shanks
> *Sent:* Thursday, February 28, 2013 5:00 PM
> *To:* Matt Hein; RobertWichert; Email question to eQuest
>
> *Subject:* Re: [Equest-users] Indoor arena suggestions/tips****
>
> ** **
>
> Matt,****
>
> ** **
>
> There is an addendum to 90.1 that adds heating-only systems 10 and 11.
> It’s addendum dn. You might check it out, but I’m not sure that your space
> really fits into that addendum, and I don’t think it helps you. When using
> that addendum, you model no cooling at all in either case. In reality, in
> the proposed building, you are getting some free cooling from natural
> ventilation. ****
>
> ** **
>
> I have an idea that’s complicated but maybe other people have a simplified
> method that will accomplish something similar. If you were going to
> accurately demonstrate what you’re saving over the baseline, you need to
> figure out how much energy your baseline system would use to do what the
> free cooling with natural ventilation is doing in the proposed model. Maybe
> you could figure out the space temperature you can achieve for each hour
> that you’re using natural ventilation for free cooling. Then, you could set
> up a space setpoint schedule in your baseline that would match those
> temperatures. The mechanical cooling system in your baseline model would
> cool to those same temperatures. Does that sound crazy? ****
>
> ** **
>
> [image: cid:image001.png at 01CE0924.38506AB0]****
>
> *Stormy L. Shanks, PE
> *Mechanical Engineer****
>
> 2882 106th St, Des Moines, IA 50322****
>
> web <http://www.kjww.com/> | Facebook<http://www.facebook.com/kjwwengineering>|
> Twitter <http://twitter.com/kjww> | LinkedIn<http://www.linkedin.com/company/kjww-engineering-consultants>
> ****
>
> ** **
>
> ** **
>
> *From:* equest-users-bounces at lists.onebuilding.org
> [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Matt
> Hein
> *Sent:* Thursday, February 28, 2013 10:24 AM
> *To:* RobertWichert; Email question to eQuest
> *Subject:* Re: [Equest-users] Indoor arena suggestions/tips****
>
> ** **
>
> Has anyone been able to capture savings from a natural ventilation design
> for LEED 2009 NC? (I interpret that G3.1.1.b prevents this.)
>
> Glancing over Appendix G I see something that doesn't seem very
> encouraging of 'green' design: (not to say that it discourages) ****
>
> - G3.1.1.b says, "All conditioned spaces in the proposed design shall
> be simulated as being both heated and cooled even if no heating or cooling
> system is to be installed ..."****
>
> It seems like there should be some way to encourage natural ventilation
> design by accounting for the energy savings.
> I suspect I'll approach this by setting a high Tstat value (100 F) and
> using the exact same cooling configuration for proposed and baseline so the
> savings are null. Well, maybe I can get some fan power savings.****
>
> - MRH****
>
>
> On 2/28/2013 8:33 AM, RobertWichert wrote:****
>
> I would certainly bring it up. I would expect it to be more comfortable
> and with much lower fuel costs. Even first cost could be lower, if you
> really plan to heat all that air, unless the insulation is very heavy, even
> on the roof. I would think you could get away with minimal insulation on
> the roof if you used radiant.
>
> Just my first thought though, I'm sure there is much more to consider.
>
>
> Maybe you could keep us apprised of your progress...
>
>
>
> ****
>
> Robert Wichert P.Eng. LEED AP BD&C****
>
> +1 916 966 9060****
>
> FAX +1 916 966 9068****
>
> ** **
>
> ** **
>
> ** **
>
> ** **
>
> ** **
>
> ** **
>
> ** **
>
> ===============================================****
>
> On 2/27/2013 2:47 PM, Matt Hein wrote:****
>
> The preliminary design calls for forced-air with low winter setpoint of
> 60F and additional fans to de-stratify. Summer is Nat. ventilation with no
> cooling.
> I plan on discussing radiant heat in our next conversation.
>
> Thanks Robert,
>
> - MRH
>
> On 2/27/2013 4:02 PM, RobertWichert wrote:****
>
> Is radiant heating being discussed, Matt?
>
>
> ****
>
> Robert Wichert P.Eng. LEED AP BD&C****
>
> +1 916 966 9060****
>
> FAX +1 916 966 9068****
>
> ** **
>
> ** **
>
> ** **
>
> ** **
>
> ** **
>
> ** **
>
> ** **
>
> ===============================================****
>
> On 2/27/2013 1:27 PM, Matt Hein wrote:****
>
> Thanks David and Nick. Your advice is much appreciated.
>
> - MRH
>
>
>
> On 2/27/2013 1:58 PM, Nick Caton wrote:****
>
> No direct answers, but I would plan on a long discussion with the HVAC
> designers to arrive at a mutual understanding of the “conditioned volume”
> and loads incident on that volume to be addressed by the systems.
> Approaching this as thermally-connected conditioned/unconditioned zones
> matching those design parameters makes sense procedurally from an eQuest
> standpoint. ****
>
> ****
>
> Time permitting, running an early “test” model to ensure the results
> agree/ballpark with the designer’s calculations would be a good idea as
> well to nail down the nuts & bolts of your modeling procedure before crunch
> time (Keeping good notes & written communication will also be helpful later
> for model documentation).****
>
> ****
>
> [image: cid:489575314 at 22072009-0ABB]****
>
> * *****
>
> *NICK CATON, P.E.*****
>
> SENIOR ENGINEER****
>
> ****
>
> Smith & Boucher Engineers****
>
> 25501 west valley parkway, suite 200****
>
> olathe, ks 66061****
>
> direct 913.344.0036****
>
> fax 913.345.0617****
>
> www.smithboucher.com* *****
>
> ****
>
> *From:* equest-users-bounces at lists.onebuilding.org [
> mailto:equest-users-bounces at lists.onebuilding.org<equest-users-bounces at lists.onebuilding.org>]
> *On Behalf Of *Matt Hein
> *Sent:* Wednesday, February 27, 2013 10:32 AM
> *To:* Email question to eQuest
> *Subject:* [Equest-users] Indoor arena suggestions/tips****
>
> ****
>
> Hello all,
>
> I'm working on an 150,000 sf indoor practice facility with 90 ft ceilings.
> Does anyone have any suggestions/tips/heads-up comments that would be
> useful in starting this model?
> Specifically, I'm wondering if I'll run into issues related to
> stratification and need to create 'sub-zones' so eQuest better represents
> the proposed distribution system.
>
> Thank you for your time and combined insight,
>
> *Matthew Hein*, P.E.
> BTU Engineering, Inc.
> 2021 25th Ave.
> Brookings, SD 57006
>
> Direct Phone: 605.695.8582
> Toll Free: 888.288.2126
> Fax: 888.288.2139
> matthew.hein at btu-engineering.com <hein at BTU-Engineering.com>****
>
> www.BTU-Engineering.com <http://www.btu-engineering.com/>
>
> LinkedIn<http://www.linkedin.com/company/2439091?utm_source=BTU+Engineering+Subscribers&utm_campaign=2c63bd2c50-Hello_from_BTU2_15_2013&utm_medium=email>
> | Facebook<https://www.facebook.com/BTU.Engineering?utm_source=BTU+Engineering+Subscribers&utm_campaign=2c63bd2c50-Hello_from_BTU2_15_2013&utm_medium=email>
> | Google+
> <https://plus.google.com/112692580402915348575/posts?utm_source=BTU+Engineering+Subscribers&utm_campaign=2c63bd2c50-Hello_from_BTU2_15_2013&utm_medium=email> |
> Twitter<https://twitter.com/BTUEngineering?utm_source=BTU+Engineering+Subscribers&utm_campaign=2c63bd2c50-Hello_from_BTU2_15_2013&utm_medium=email>
> | Subscribe to Email List <http://eepurl.com/uWeS9>****
>
> ** **
>
> On 2/27/2013 10:50 AM, David Eldridge wrote:****
>
> eQUEST will assume a uniform temperature throughout the zone, so if the
> proposed HVAC system will allow stratification then you would need to do
> something like you are describing.****
>
> ****
>
> David****
>
> *
> *****
>
> ****
>
> David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP****
>
> *Grumman/Butkus Associates*****
>
> *
> *****
>
> ****
>
> ****
>
>
>
> ****
>
> _______________________________________________****
>
> Equest-users mailing list****
>
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org****
>
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG****
>
> ** **
>
> ** **
>
> ** **
>
> ** **
>
> ** **
> ------------------------------
>
> *This message and any attachments contain information intended for a
> specific party and may include sensitive or confidential material. If you
> are not the intended recipient, please do not read, copy, use, or disclose
> to others. Please notify the sender of the delivery error by reply and then
> permanently delete this message and all attachments.*
> ****
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130301/8a73045b/attachment.htm>
More information about the Equest-users
mailing list