[Equest-users] Weather Data HCMC Vietnam, was Re: Indoor arena suggestions/tips
Joe Huang
yjhuang at whiteboxtechnologies.com
Fri Mar 15 23:40:55 PDT 2013
Kieu Anh,
There is an IWEC2 weather file for Ho Chi Minh City, as well as 18 other
locations in Vietnam (see attached JPG taken from my Web site).
The entire set of IWEC2 weather files for 3,012 international locations,
i.e., excluding the US and Canada, is available on a DVD from ASHRAE
for $229 (see www.techstreet.com/cgi-bin/detail?product_id=1823067 for
details).
Inidividual IWEC2 files are now also available from my company, White
Box Technologies, for $35, payable through PayPal. Please contact me
for details.
BTW, I changed the subject line to reflect better the content of your
post. I don't look at all the posts on the bulletin board, but will
generally look at the ones having to do with weather data, which is why
I didn't see your question until now.
Joe
On 3/1/2013 1:54 AM, Kieu Anh Doan wrote:
> Dear All,
>
> I'm a beginner for eQuest stimulation. Now I'm starting the software
> for my Greenhouse 1200 sf area, 6 ft high. Unfortunately my location
> is Ho Chi Minh City, Vietnam that there's no weather data to be put in
> for use. Could anyone please help me to start?
>
> Doan Kieu Anh,
>
> Ho Chi Minh City, Vietnam
> Cell: +8498 559 1925
>
>
>
> On Fri, Mar 1, 2013 at 7:12 AM, Nathan Kegel <nathan.kegel at iesve.com
> <mailto:nathan.kegel at iesve.com>> wrote:
>
> I don't think this prevents you from taking credit for natural
> ventilation. It doesn't say you must provide fans, pumps,
> diffusers, etc. You CAN heat and cool with an open window after
> all -- although cooling is the far more common application of
> natural ventilation. J
>
> What you would need is a way to model space temperature and
> control the windows (plus any other devices to mechanically
> condition the space when conditions weren't favourable for natural
> ventilation) to maintain the comfort range. There are tools that
> allow you to control windows and HVAC systems in this manner --
> based on space temperature, CO2 level, humidity, etc. So assuming
> your space type and climate are good fits for this strategy -- you
> can apply the appropriate software and control "sequences" to
> model a system in accordance with Appendix G -- and account for
> wind speed, wind direction, temperatures, moisture, etc. in a
> fully dynamic fashion.
>
> While I've never attempted to use eQuest for this, I have taken
> this approach successfully with tools that are intended to model
> these types of systems.
>
> Description: IES <http://www.iesve.com/>
>
>
>
> *Nathan Kegel*
> *Project Manager*
>
> *Business Development Manager*
>
> Minneapolis
>
>
>
> T:
>
>
>
> 763 276 9981 <tel:763%20276%209981>
>
> M:
>
>
>
> 415 420 9314 <tel:415%20420%209314>
>
> http://www.iesve.com <http://www.iesve.com/>
>
> **Design, Simulate + Innovate with the *<Virtual Environment>***
>
> Integrated Environmental Solutions Limited. Registered in Scotland
> No. SC151456
> Registered Office - Helix Building, West Of Scotland Science Park,
> Glasgow G20 0SP
>
> Email Disclaimer <http://www.iesve.com/disclaimer.html>
>
> *From:*equest-users-bounces at lists.onebuilding.org
> <mailto:equest-users-bounces at lists.onebuilding.org>
> [mailto:equest-users-bounces at lists.onebuilding.org
> <mailto:equest-users-bounces at lists.onebuilding.org>] *On Behalf Of
> *Stormy L. Shanks
> *Sent:* Thursday, February 28, 2013 5:00 PM
> *To:* Matt Hein; RobertWichert; Email question to eQuest
>
>
> *Subject:* Re: [Equest-users] Indoor arena suggestions/tips
>
> Matt,
>
> There is an addendum to 90.1 that adds heating-only systems 10 and
> 11. It's addendum dn. You might check it out, but I'm not sure
> that your space really fits into that addendum, and I don't think
> it helps you. When using that addendum, you model no cooling at
> all in either case. In reality, in the proposed building, you are
> getting some free cooling from natural ventilation.
>
> I have an idea that's complicated but maybe other people have a
> simplified method that will accomplish something similar. If you
> were going to accurately demonstrate what you're saving over the
> baseline, you need to figure out how much energy your baseline
> system would use to do what the free cooling with natural
> ventilation is doing in the proposed model. Maybe you could figure
> out the space temperature you can achieve for each hour that
> you're using natural ventilation for free cooling. Then, you could
> set up a space setpoint schedule in your baseline that would match
> those temperatures. The mechanical cooling system in your baseline
> model would cool to those same temperatures. Does that sound crazy?
>
> cid:image001.png at 01CE0924.38506AB0
>
>
>
> *Stormy L. Shanks, PE
> *Mechanical Engineer
>
> 2882 106^th St, Des Moines, IA 50322
>
> web <http://www.kjww.com/> | Facebook
> <http://www.facebook.com/kjwwengineering> | Twitter
> <http://twitter.com/kjww> | LinkedIn
> <http://www.linkedin.com/company/kjww-engineering-consultants>
>
> *From:*equest-users-bounces at lists.onebuilding.org
> <mailto:equest-users-bounces at lists.onebuilding.org>
> [mailto:equest-users-bounces at lists.onebuilding.org]
> <mailto:[mailto:equest-users-bounces at lists.onebuilding.org]> *On
> Behalf Of *Matt Hein
> *Sent:* Thursday, February 28, 2013 10:24 AM
> *To:* RobertWichert; Email question to eQuest
> *Subject:* Re: [Equest-users] Indoor arena suggestions/tips
>
> Has anyone been able to capture savings from a natural ventilation
> design for LEED 2009 NC? (I interpret that G3.1.1.b prevents this.)
>
> Glancing over Appendix G I see something that doesn't seem very
> encouraging of 'green' design: (not to say that it discourages)
>
> * G3.1.1.b says, "All conditioned spaces in the proposed design
> shall be simulated as being both heated and cooled even if no
> heating or cooling system is to be installed ..."
>
> It seems like there should be some way to encourage natural
> ventilation design by accounting for the energy savings.
> I suspect I'll approach this by setting a high Tstat value (100 F)
> and using the exact same cooling configuration for proposed and
> baseline so the savings are null. Well, maybe I can get some fan
> power savings.
>
> - MRH
>
>
> On 2/28/2013 8:33 AM, RobertWichert wrote:
>
> I would certainly bring it up. I would expect it to be more
> comfortable and with much lower fuel costs. Even first cost
> could be lower, if you really plan to heat all that air,
> unless the insulation is very heavy, even on the roof. I
> would think you could get away with minimal insulation on the
> roof if you used radiant.
>
> Just my first thought though, I'm sure there is much more to
> consider.
>
>
> Maybe you could keep us apprised of your progress...
>
>
>
> Robert Wichert P.Eng. LEED AP BD&C
>
> +1 916 966 9060 <tel:%2B1%20916%20966%209060>
>
> FAX+1 916 966 9068 <tel:%2B1%20916%20966%209068>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
> ===============================================
>
> On 2/27/2013 2:47 PM, Matt Hein wrote:
>
> The preliminary design calls for forced-air with low
> winter setpoint of 60F and additional fans to de-stratify.
> Summer is Nat. ventilation with no cooling.
> I plan on discussing radiant heat in our next conversation.
>
> Thanks Robert,
>
> - MRH
>
> On 2/27/2013 4:02 PM, RobertWichert wrote:
>
> Is radiant heating being discussed, Matt?
>
>
> Robert Wichert P.Eng. LEED AP BD&C
>
> +1 916 966 9060 <tel:%2B1%20916%20966%209060>
>
> FAX+1 916 966 9068 <tel:%2B1%20916%20966%209068>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
> ===============================================
>
> On 2/27/2013 1:27 PM, Matt Hein wrote:
>
> Thanks David and Nick. Your advice is much
> appreciated.
>
> - MRH
>
>
>
> On 2/27/2013 1:58 PM, Nick Caton wrote:
>
> No direct answers, but I would plan on a long
> discussion with the HVAC designers to arrive
> at a mutual understanding of the "conditioned
> volume" and loads incident on that volume to
> be addressed by the systems. Approaching this
> as thermally-connected
> conditioned/unconditioned zones matching those
> design parameters makes sense procedurally
> from an eQuest standpoint.
>
> Time permitting, running an early "test" model
> to ensure the results agree/ballpark with the
> designer's calculations would be a good idea
> as well to nail down the nuts & bolts of your
> modeling procedure before crunch time (Keeping
> good notes & written communication will also
> be helpful later for model documentation).
>
> cid:489575314 at 22072009-0ABB
>
> **
>
> *NICK CATON, P.E.*
>
> SENIOR ENGINEER
>
> Smith & Boucher Engineers
>
> 25501 west valley parkway, suite 200
>
> olathe, ks 66061
>
> direct 913.344.0036 <tel:913.344.0036>
>
> fax 913.345.0617 <tel:913.345.0617>
>
> www.smithboucher.com
> <http://www.smithboucher.com>__
>
> *From:*equest-users-bounces at lists.onebuilding.org
> <mailto:equest-users-bounces at lists.onebuilding.org>
> [mailto:equest-users-bounces at lists.onebuilding.org]
> *On Behalf Of *Matt Hein
> *Sent:* Wednesday, February 27, 2013 10:32 AM
> *To:* Email question to eQuest
> *Subject:* [Equest-users] Indoor arena
> suggestions/tips
>
> Hello all,
>
> I'm working on an 150,000 sf indoor practice
> facility with 90 ft ceilings. Does anyone have
> any suggestions/tips/heads-up comments that
> would be useful in starting this model?
> Specifically, I'm wondering if I'll run into
> issues related to stratification and need to
> create 'sub-zones' so eQuest better represents
> the proposed distribution system.
>
> Thank you for your time and combined insight,
>
> *Matthew Hein*, P.E.
> BTU Engineering, Inc.
> 2021 25^th Ave.
> Brookings, SD 57006
>
> Direct Phone: 605.695.8582 <tel:605.695.8582>
> Toll Free: 888.288.2126 <tel:888.288.2126>
> Fax: 888.288.2139 <tel:888.288.2139>
> matthew.hein at btu-engineering.com
> <mailto:hein at BTU-Engineering.com>
>
> www.BTU-Engineering.com
> <http://www.btu-engineering.com/>
>
> LinkedIn
> <http://www.linkedin.com/company/2439091?utm_source=BTU+Engineering+Subscribers&utm_campaign=2c63bd2c50-Hello_from_BTU2_15_2013&utm_medium=email>
> | Facebook
> <https://www.facebook.com/BTU.Engineering?utm_source=BTU+Engineering+Subscribers&utm_campaign=2c63bd2c50-Hello_from_BTU2_15_2013&utm_medium=email>
> | Google+
> <https://plus.google.com/112692580402915348575/posts?utm_source=BTU+Engineering+Subscribers&utm_campaign=2c63bd2c50-Hello_from_BTU2_15_2013&utm_medium=email> |
> Twitter
> <https://twitter.com/BTUEngineering?utm_source=BTU+Engineering+Subscribers&utm_campaign=2c63bd2c50-Hello_from_BTU2_15_2013&utm_medium=email>
> | Subscribe to Email List
> <http://eepurl.com/uWeS9>
>
> On 2/27/2013 10:50 AM, David Eldridge wrote:
>
> eQUEST will assume a uniform temperature
> throughout the zone, so if the proposed HVAC
> system will allow stratification then you
> would need to do something like you are
> describing.
>
> David
>
> __
>
> David S. Eldridge, Jr., P.E., LEED AP BD+C,
> BEMP, BEAP, HBDP
>
> *Grumman/Butkus Associates*
>
> __
>
>
>
> _______________________________________________
>
> Equest-users mailing list
>
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>
> To unsubscribe from this mailing list send a blank message toEQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG <mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
>
> ------------------------------------------------------------------------
>
> /This message and any attachments contain information intended for
> a specific party and may include sensitive or confidential
> material. If you are not the intended recipient, please do not
> read, copy, use, or disclose to others. Please notify the sender
> of the delivery error by reply and then permanently delete this
> message and all attachments./
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
> <mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130315/7aff105a/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: vietnam_iwec2.jpg
Type: image/jpeg
Size: 138593 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130315/7aff105a/attachment-0002.jpg>
More information about the Equest-users