[Equest-users] Modeling site obstructions for EAp2c1
Arpan Bakshi
arpanbakshi at gmail.com
Wed Mar 20 11:27:27 PDT 2013
Demba, unfortunately, the User's Manual cannot be used as the word of the
rating authority. It would need to be cited somewhere in the Standard, or
in a ruling by the GBCI.
*Arpan Bakshi** *LEED AP BD+C, ESTIDAMA PQP
On Wed, Mar 20, 2013 at 2:25 PM, Demba Ndiaye <Demba.Ndiaye at setty.com>wrote:
> Arpan, ****
>
> ** **
>
> The 90.1-2007 User’s Manual clearly states (page G-15): ****
>
> ** **
>
> *“Shading of the building by surrounding structures and topography should
> be modeled identically in both the proposed and baseline buildings.”*
>
> ** **
>
> Which confirms what you have grasped.****
>
> ** **
>
> Regards,****
>
> ** **
>
> ***** *
>
> **[image: S&A Logo]***Demba Ndiaye, Ph.D., P.E., LEED AP BD+C, BEMP*****
>
> *Senior Energy Analyst/Mechanical Engineer*****
>
> * *
>
> *Setty & Associates, Ltd.*
>
> ** **
>
> MEP Design Engineering | Project Management ****
>
> |Construction Management | Design-Build Services | Commissioning ****
>
> |3040 Williams Drive, Suite 600 | Fairfax, VA 22031 ****
>
> |Voice 703.691.2115 | Fax 703.691.8084 | cell 571.830.9913 ****
>
> demba.ndiaye at setty.com | www.setty.com****
>
> ** **
>
> This e-mail and any files transmitted with it are confidential and are
> intended solely for the use of the individual or entity to whom they are
> addressed. If you are NOT the intended recipient or the person responsible
> for delivering the e-mail to the intended recipient, be advised that you
> have received this e-mail in error and that any use, dissemination,
> forwarding, printing or copying this e-mail is strictly prohibited.****
>
> ** **
>
> ** **
>
> ** **
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Arpan Bakshi
> *Sent:* Wednesday, March 20, 2013 12:53 PM
> *To:* equest-users
> *Subject:* [Equest-users] Modeling site obstructions for EAp2c1****
>
> ** **
>
> All,****
>
> ** **
>
> I have learned through informal conversations that modeling site
> obstructions from (surrounding buildings) is fine by GBCI, so long as there
> is consistency and the same approach is taken in both Baseline and Proposed
> models, i.e. either both models include surrounding buildings, nor neither
> does.****
>
> ** **
>
> Is there a CIR or other reference anyone is familiar with which records
> this guidance, which can be cited?****
>
> ** **
>
> Thanks.****
>
>
> ****
>
> ****
>
> *Arpan Bakshi *LEED AP BD+C, ESTIDAMA PQP****
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130320/81b1ee49/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 167 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130320/81b1ee49/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2912 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130320/81b1ee49/attachment-0002.jpeg>
More information about the Equest-users
mailing list