[Equest-users] Baseline Fan power calculation
Nick Caton
ncaton at smithboucher.com
Mon Mar 25 08:49:31 PDT 2013
Thanks Maria, and wow!
I remember first seeing the previous LEED v3 EAp2 spreadsheets for the first time and thinking "WOW, this is intense" ... I had no idea what was coming!
I appreciate the heads up - this will require some heavy review before my next new LEED project to adjust my workflow & supporting calculations. Playing around just a bit, this spreadsheet looks to have its own 'learning curve' to utilize, like some of the LEED Online templates over time, but being excel perhaps this is more easy to troubleshoot/work around...
Regards,
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: Maria Karpman [mailto:maria.karpman at karpmanconsulting.net]
Sent: Monday, March 25, 2013 10:25 AM
To: 'Bishop, Bill'; 'RobertWichert'; Nick Caton; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Baseline Fan power calculation
FYI, the newest LEED EAp2 spreadsheet (attached) has embedded calculations for the baseline fan power on Air-Side HVAC Details tab, which I think is quite handy.
Maria
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Bishop, Bill
Sent: Monday, March 25, 2013 11:01 AM
To: RobertWichert; Nick Caton; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Baseline Fan power calculation
Robert,
I'm sure Nick is typing furiously as I write this, but I'll probably finish before him.
Taking a quick look at the spreadsheet that Nick attached to his email, it calculates baseline fan power using the method described in Appendix G and 6.5.3.1.1. Fan efficiency is included in the Pfan calculation per G3.1.2.9.
Fan efficiency is from ASHRAE 90.1, Table 10.8 as described in G3.1.2.9.
Regards,
Bill
William Bishop, PE, BEMP, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 325-6004 Ext. 114 F: (585) 325-6005
wbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
P Sustainability - the forest AND the trees. P
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of RobertWichert
Sent: Monday, March 25, 2013 10:52 AM
To: Nick Caton; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Baseline Fan power calculation
I believe I have written about this in the past, but since this seems to be on-topic, I'll bring it up again.
The theoretical fan power equation, Fan BHP = (cfm x static press "w.c.) / (6356 x fan efficiency) can be used to calculate the theoretical fan BHP, but you need the fan efficiency. This seems to be NOT the way the BHP is being calculated by the spreadsheet that was attached previously.
Is there a reason for that?
Was there an assumed fan efficiency used in the spreadsheet, and was it based on anything particular, or just a conservative assumption?
Thanks!
Robert Wichert P.Eng. LEED AP BD&C
+1 916 966 9060
FAX +1 916 966 9068
===============================================
On 3/25/2013 7:34 AM, Nick Caton wrote:
Hi Vamshi,
I advise carefully reviewing the footnotes under Table 6.5.3.1.1A, which include procedure for determining baseline fan power adjustments.
1. Pfan represents the sum power of all fans in a given baseline system (with exception to baseline systems #6/#8, fan powered VAV boxes).
2. Again, there is not a separate supply/return power calculation (see answer #1). You can however account for adjustments present in separate airstreams from the proposed design.
3. Probably not. Review the difference between CFMS and CFMD carefully at the cited Table. A CFM quantity representing the airflow each element encounters (CFMD) should be applied against each pressure drop adjustment, not an 'aggregate' of supply+return.
You may also find the attached resource published by 7group helpful to cement your procedural understanding of how to arrive at the sum total for "A."
Regards,
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of vamshi ranga
Sent: Monday, March 25, 2013 8:17 AM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Baseline Fan power calculation
Hi All,
I have a doubt regarding calculating fan power as per ASHRAE 90.1-2007.
My proposed system has, supply return and exhaust fans separately with kW and cfm mentioned for each fan.
So, for calculating baseline fan power,
1. should I calculate it separately for each fan type?
2. can I take pressure drop adjustment both in supply and return fan power calculation?
3. should I sum all the cfms of supply, return and exhaust and than apply pressure drop adjustments to aggregated cfm.
Kindly help me out in solving the doubt. If you have any example fan power calculations, or web links those could guide me regarding this, plz do share them.
Thanks in advance.
Regards,
Vamshi.
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
________________________________
No virus found in this message.
Checked by AVG - www.avg.com<http://www.avg.com>
Version: 2012.0.2240 / Virus Database: 2641/5703 - Release Date: 03/25/13
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130325/37fe38fc/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130325/37fe38fc/attachment-0002.jpg>
More information about the Equest-users
mailing list