[Equest-users] Baseline Fan power calculation
RobertWichert
robert at wichert.org
Mon Mar 25 09:31:30 PDT 2013
It seems to just sum them up in cell M29. Is that what you meant,
Maria? I don't see any calculations, they just ask for you to input the
fan power.
Am I missing something?
Robert Wichert P.Eng. LEED AP BD&C
+1 916 966 9060
FAX +1 916 966 9068
===============================================
On 3/25/2013 8:24 AM, Maria Karpman wrote:
>
> FYI, the newest LEED EAp2 spreadsheet (attached) has embedded
> calculations for the baseline fan power on Air-Side HVAC Details tab,
> which I think is quite handy.
>
> Maria
>
> *From:*equest-users-bounces at lists.onebuilding.org
> [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf Of
> *Bishop, Bill
> *Sent:* Monday, March 25, 2013 11:01 AM
> *To:* RobertWichert; Nick Caton; equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] Baseline Fan power calculation
>
> Robert,
>
> I'm sure Nick is typing furiously as I write this, but I'll probably
> finish before him.
>
> Taking a quick look at the spreadsheet that Nick attached to his
> email, it calculates baseline fan power using the method described in
> Appendix G and 6.5.3.1.1. Fan efficiency is included in the P_fan
> calculation per G3.1.2.9.
>
> Fan efficiency is from ASHRAE 90.1, Table 10.8 as described in G3.1.2.9.
>
> Regards,
>
> Bill
>
> *William Bishop, PE, BEMP, LEED AP **|**Pathfinder Engineers &
> Architects LLP*
>
> Senior Energy Engineer
>
> 134 South Fitzhugh StreetRochester, NY 14608
>
> T: (585) 325-6004 Ext. 114F: (585) 325-6005
>
> wbishop at pathfinder-ea.com
> <mailto:wbishop at pathfinder-ea.com>www.pathfinder-ea.com
> <http://www.pathfinder-ea.com/>
>
> PSustainability -- the forest AND the trees.P
>
> *From:*equest-users-bounces at lists.onebuilding.org
> <mailto:equest-users-bounces at lists.onebuilding.org>
> [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf Of
> *RobertWichert
> *Sent:* Monday, March 25, 2013 10:52 AM
> *To:* Nick Caton; equest-users at lists.onebuilding.org
> <mailto:equest-users at lists.onebuilding.org>
> *Subject:* Re: [Equest-users] Baseline Fan power calculation
>
> I believe I have written about this in the past, but since this seems
> to be on-topic, I'll bring it up again.
>
> The theoretical fan power equation, Fan BHP = (cfm x static press
> "w.c.) / (6356 x fan efficiency) can be used to calculate the
> theoretical fan BHP, but you need the fan efficiency. This seems to
> be NOT the way the BHP is being calculated by the spreadsheet that was
> attached previously.
>
> Is there a reason for that?
>
> Was there an assumed fan efficiency used in the spreadsheet, and was
> it based on anything particular, or just a conservative assumption?
>
>
> Thanks!
>
>
>
> Robert Wichert P.Eng. LEED AP BD&C
> +1 916 966 9060
> FAX +1 916 966 9068
>
>
>
>
>
>
>
> ===============================================
>
> On 3/25/2013 7:34 AM, Nick Caton wrote:
>
> Hi Vamshi,
>
> I advise carefully reviewing the footnotes under Table 6.5.3.1.1A,
> which include procedure for determining baseline fan power
> adjustments.
>
> 1.P_fan represents the sum power of all fans in a given baseline
> system (with exception to baseline systems #6/#8, fan powered VAV
> boxes).
>
> 2.Again, there is not a separate supply/return power calculation
> (see answer #1). You can however account for adjustments present
> in separate airstreams from the proposed design.
>
> 3.Probably not. Review the difference between CFM_S and CFM_D
> carefully at the cited Table. A CFM quantity representing the
> airflow each element encounters (CFM_D ) should be applied against
> each pressure drop adjustment, not an 'aggregate' of supply+return.
>
> You may also find the attached resource published by 7group
> helpful to cement your procedural understanding of how to arrive
> at the sum total for "A."
>
> Regards,
>
> ~Nick
>
> cid:489575314 at 22072009-0ABB
>
> **
>
> *NICK CATON, P.E.*
>
> SENIOR ENGINEER
>
> Smith & Boucher Engineers
>
> 25501 west valley parkway, suite 200
>
> olathe, ks 66061
>
> direct 913.344.0036
>
> fax 913.345.0617
>
> www.smithboucher.com__
>
> *From:*equest-users-bounces at lists.onebuilding.org
> <mailto:equest-users-bounces at lists.onebuilding.org>
> [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf Of
> *vamshi ranga
> *Sent:* Monday, March 25, 2013 8:17 AM
> *To:* equest-users at lists.onebuilding.org
> <mailto:equest-users at lists.onebuilding.org>
> *Subject:* [Equest-users] Baseline Fan power calculation
>
> Hi All,
>
> I have a doubt regarding calculating fan power as per ASHRAE
> 90.1-2007.
>
> My proposed system has, supply return
> and exhaust fans separately with kW and cfm mentioned for each fan.
>
> So, for calculating baseline fan power,
>
> 1. should I calculate it separately for each fan type?
>
> 2. can I take pressure drop adjustment both in supply and return
> fan power calculation?
>
> 3. should I sum all the cfms of supply, return and exhaust and
> than apply pressure drop adjustments to aggregated cfm.
>
> Kindly help me out in solving the doubt. If you have any example
> fan power calculations, or web links those could guide me
> regarding this, plz do share them.
>
> Thanks in advance.
>
> Regards,
>
> Vamshi.
>
>
>
> _______________________________________________
>
> Equest-users mailing list
>
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>
> To unsubscribe from this mailing list send a blank message toEQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG <mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
>
> ------------------------------------------------------------------------
>
> No virus found in this message.
> Checked by AVG - www.avg.com <http://www.avg.com>
> Version: 2012.0.2240 / Virus Database: 2641/5703 - Release Date: 03/25/13
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130325/0693d62c/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130325/0693d62c/attachment-0002.jpeg>
More information about the Equest-users
mailing list