Wed May 15 08:06:44 PDT 2013
Paul,
You should be able to model that by entering negative Input Power Btu/h
under Internal Energy Source on the Equipment tab of the Space Properties
window:
I used it on a few occasions to capture impact of externally calculated
process loads such as refrigeration equipment with remote condensers.
Maria
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Paul Diglio
Sent: Wednesday, May 15, 2013 10:38 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Modeling False AC Load
Folks:
I am modeling a chilled beam demonstration area. In one room the owner will
be installing a split AC system with electric heat in order to provide a
false load for the chilled beams.
The primary air to the 3 chilled beams is provided via VAV terminals from an
ERU. The ERU is equipped with chilled and hot water coils.
I can simulate a false cooling load by adding equipment under the Internal
Loads tab. I don't know how to make the room colder during the summer
months in order to require more heat from the chilled beams.
Any ideas on how to simulate a false heating load into this space?
Thank you,
Paul Diglio, CEM, CBCP
87 Fairmont Avenue
New Haven, CT 06513
203-415-0082
www.pdigliollc.com
_____
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.2242 / Virus Database: 3162/5825 - Release Date: 05/15/13
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130515/2ea88aa0/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 26369 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130515/2ea88aa0/attachment-0002.jpeg>
More information about the Equest-users
mailing list