[Equest-users] Question on LS-C report
Morteza Kasmai
morteza.kasmai at gmail.com
Tue Nov 12 09:52:42 PST 2013
Bill,
Thank you so much for your respond. Total number of occupants, schedules
and infiltration rates are the same for the base and the proposed model and
I was wondering if the related loads reported in LS-C should be also the
same.
Regards,
Morteza
On Tue, Nov 12, 2013 at 11:39 AM, Bishop, Bill <bbishop at pathfinder-ea.com>wrote:
> Morteza,
>
>
>
> The occupant and infiltration loads reported on LS-C do not have to match
> between baseline and proposed. Just make sure your number of occupants,
> infiltration rate, and schedules are the same. Total occupants is easy to
> compare using the LV-B report. The numbers on LS-C may not match between
> baseline and proposed, especially when the date/time of the peak cooling
> and heating loads are different.
>
>
>
> Regards,
>
> Bill
>
>
>
> *William Bishop, PE, BEMP, BEAP, LEED AP **|** Pathfinder Engineers &
> Architects LLP*
>
> *Senior Energy Engineer*
>
> [image: webCertified_logo_colorRGB72DPI.jpg]
>
>
>
> 134 South Fitzhugh Street Rochester, NY 14608
>
> T: (585) 325-6004 Ext. 114 F: (585) 325-6005
>
> bbishop at pathfinder-ea.com <wbishop at pathfinder-ea.com>
> www.pathfinder-ea.com
>
> P Sustainability – the forest AND the trees. P
>
>
>
>
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Morteza Kasmai
> *Sent:* Monday, November 11, 2013 7:26 PM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] Question on LS-C report
>
>
>
> Hello all,
>
>
>
> I have a question regarding figures reported for “OCCUPANTS TO SPACE” and
> “INFILTRATION” in LS-C Building Peak Load Components report. When we
> compare LS-C reports of a given project, should occupants load and
> infiltration load of the baseline model be equal to the same loads of the
> proposed model?
>
>
>
> I would appreciate your comments,
>
> Morteza
>
>
>
>
>
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131112/b4ef20d2/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 3124 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131112/b4ef20d2/attachment-0002.jpeg>
More information about the Equest-users
mailing list