[Equest-users] Question on LS-C report
Robby Oylear
robbyoylear at gmail.com
Tue Nov 12 10:27:00 PST 2013
It's likely that each buildings will have a different peak load which
occurs at a unique time during the year. If the loads do not occur at the
same hour, the occupancy load will likely be different, and outside air
conditions may vary such that your infiltration load will also be different.
I'd say it is unlikely that you should ever see the occupancy and
infiltration related loads in the LS-C be identical between a baseline and
a proposed model.
-Robby
On Tue, Nov 12, 2013 at 9:52 AM, Morteza Kasmai <morteza.kasmai at gmail.com>wrote:
> Bill,
>
>
>
> Thank you so much for your respond. Total number of occupants, schedules
> and infiltration rates are the same for the base and the proposed model and
> I was wondering if the related loads reported in LS-C should be also the
> same.
>
>
>
> Regards,
>
> Morteza
>
>
>
>
>
> On Tue, Nov 12, 2013 at 11:39 AM, Bishop, Bill <bbishop at pathfinder-ea.com>wrote:
>
>> Morteza,
>>
>>
>>
>> The occupant and infiltration loads reported on LS-C do not have to match
>> between baseline and proposed. Just make sure your number of occupants,
>> infiltration rate, and schedules are the same. Total occupants is easy to
>> compare using the LV-B report. The numbers on LS-C may not match between
>> baseline and proposed, especially when the date/time of the peak cooling
>> and heating loads are different.
>>
>>
>>
>> Regards,
>>
>> Bill
>>
>>
>>
>> *William Bishop, PE, BEMP, BEAP, LEED AP **|** Pathfinder Engineers &
>> Architects LLP*
>>
>> *Senior Energy Engineer*
>>
>> [image: webCertified_logo_colorRGB72DPI.jpg]
>>
>>
>>
>> 134 South Fitzhugh Street Rochester, NY 14608
>>
>> T: (585) 325-6004 Ext. 114 F: (585) 325-6005
>>
>> bbishop at pathfinder-ea.com <wbishop at pathfinder-ea.com>
>> www.pathfinder-ea.com
>>
>> P Sustainability – the forest AND the trees. P
>>
>>
>>
>>
>>
>> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
>> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Morteza Kasmai
>> *Sent:* Monday, November 11, 2013 7:26 PM
>> *To:* equest-users at lists.onebuilding.org
>> *Subject:* [Equest-users] Question on LS-C report
>>
>>
>>
>> Hello all,
>>
>>
>>
>> I have a question regarding figures reported for “OCCUPANTS TO SPACE” and
>> “INFILTRATION” in LS-C Building Peak Load Components report. When we
>> compare LS-C reports of a given project, should occupants load and
>> infiltration load of the baseline model be equal to the same loads of the
>> proposed model?
>>
>>
>>
>> I would appreciate your comments,
>>
>> Morteza
>>
>>
>>
>>
>>
>>
>>
>>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131112/7e23b33f/attachment-0002.htm>
More information about the Equest-users
mailing list