[Equest-users] Modeling Zones with Unit heaters as per ASHRAE 90.1. Appendix G
Nathan Miller
nathanm at rushingco.com
Fri Nov 15 15:56:39 PST 2013
You could always model them as Packaged Terminal Air-Conditioners. Define the heat source to match your unit heaters (gas/electric). Then you get DX cooling.
On jobs I've worked on with electric resistance heat and no cooling, I've used the PTAC system type, zeroed out the fan-power, selected electric heat, and it was accepted by the reviewers. In that case I DID NOT separate out fan power from the cooling EER, since otherwise I would not account for the artificial fan energy in addition to the artificial cooling energy mandated by having to model a cooling system.
Nathan Miller - PE, LEED(r)AP BD+C, CEM
Mechanical Engineer/Senior Energy Analyst
RUSHING | D 206-788-4577 | O 206-285-7100
www.rushingco.com<http://www.rushingco.com/>
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Simge Andolsun
Sent: Friday, November 15, 2013 3:05 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Modeling Zones with Unit heaters as per ASHRAE 90.1. Appendix G
ASHRAE 90.1. Appendix G says that, even if a zone is heating only in the actual building, a cooling system identical to that in the baseline system should be modeled in the as-built model with intermittent fan operation to meet the loads. I have seen projects with zones that have only unit heaters with no cooling air supply. eQuest does not allow for modeling of any cooling system in a zone with a unit heater. What would be your approach to solving this problem?
I would appreciate it very much if you could help me with this question.
Thank you very much in advance for your suggestions,
Best Regards,
Simge Andolsun, PhD.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131115/95d26c34/attachment-0002.htm>
More information about the Equest-users
mailing list