[Equest-users] RCondenser Water Temp Control
Melissa Crowe
MCrowe at engsolutions.com
Thu Oct 17 08:24:44 PDT 2013
Good Morning All
I have two questions.
1. Anyone know if there is there any way to override the eQuest minimum CWS temp (60°F)? We are using centrifugal chillers with VFD that will operate with CWS temps as low as 50°F.
I found this in post from 5/6/10:
...place the commands below just before the
equipment you want to disable the limits.
" DIAGNOSTIC NO-LIMITS.."
I tried putting this before the chiller or the CW loop definition in the input file to no effect and eQuest deletes the command.
One annoyingly frustrating thing about this "low limit" is that when a "water side economizer" chiller is put on the same loop to model a free cool heat exchanger the CWS temp can go below the limit (I'm not sure how the low limit is controlled ).
This leads me to the second question:
2. Anyone know how to control the CWS temp during free cool? I have tried to use a CW reset schedule but the schedule is ignored in free cool. The warning in the eQuest, DOE2, help on the topic that it's all or nothing seems to mean auto pilot only.
Thanks in advance for your thoughts.
Melissa
[cid:image001.jpg at 01CECB2B.7B0720A0]
Melissa P. Crowe, LEED AP
Project Engineer
Engineered Solutions, Inc.
6 Union St, Natick MA 01760
508.647.9200 x225 (P) l 508.652.1936 (F)
MCrowe at EngSolutions.com<mailto:MCrowe at EngSolutions.com>
CAUTION: The preceding email message and any attachments to it may be confidential and/or may contain proprietary information that is entitled to protection from disclosure under applicable law. It is not intended for transmission to, or receipt by, any unauthorized persons. If you are not the intended recipient or such recipient's employee or agent, please do not read any attachments, or print, copy, disseminate or otherwise disclose the contents of this email. If you have received this message in error, please (i) notify the sender by return email immediately that you received the message in error, and (ii) erase or destroy the message.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131017/2a2be4d8/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1517 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131017/2a2be4d8/attachment.jpg>
More information about the Equest-users
mailing list