[Equest-users] BUILDING-LOADS Hourly outputs
Eric Wilson
ericjhwilson at gmail.com
Wed Sep 4 10:49:56 PDT 2013
Nevermind, I was confused because I was actually looking at
SYSTEMS/BUILDING-HVAC Total cooling load (Btu/hr).
Eric
On Wed, Sep 4, 2013 at 9:48 AM, Eric Wilson <ericjhwilson at gmail.com> wrote:
> I have a question about the hourly loads documented in Volume 4: Libraries
> & Reports > Reports > Hourly-Report and REPORT-BLOCK:
>
> If I compare monthly sums for BUILDING-LOADS Variable 19 "Building cooling
> load (sensible)" to the monthly sensible cooling energy values in Report
> SS-I, I do not get agreement. However, the sensible load monthly sums do
> agree with the *total* cooling energy (sum of sensible and latent
> columns) in Report SS-I.
>
> This makes me think that Variable 19 is mistakenly reporting the total
> cooling load. Has anyone seen this before? Relevant files are attached.
>
> Thanks,
> Eric
>
> Eric Wilson
> Engineer, Residential Buildings Research Group
> National Renewable Energy Laboratory
> 303-275-4676
> eric.wilson at nrel.gov
>