I don't think there is a direct way to do this. Could you just run it with zero outside air and see the difference?

Another way I guess would be to subtract the space loads from the system loads - which would in theory get you the ventilation loads. This won't actually tell you how much energy is being used to meet that load though.  Much simpler to zero out the OA.

Vikram Sami
Associate Partner



ZGF ARCHITECTS LLP
T 206.521.3509 E vikram.sami at zgf.com
925 Fourth Avenue, Suite 2400
Seattle, WA 98104


From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Pasha Korber-Gonzalez
Sent: Wednesday, September 11, 2013 1:28 PM
To: The Watt Doctors - Dave Weigel
Cc: eQuest Users
Subject: Re: [Equest-users] Ventilation Energy

Hi Dave,   I use the quick and dirty way for peak vent loads from the SV-A report using the multiplier of the supply cfm and the OA% values at the top of the report.  You can also compare the peak Vent CFM at the zone level at the bottom of the report where they show the OA CFM for each zone.

Does anybody else use hourly reports to compile the Ventilation data?

Pasha
www.korberenergyconsultants.com<http://www.korberenergyconsultants.com>


On Wed, Sep 11, 2013 at 1:21 PM, The Watt Doctors - Dave Weigel <Dave.Weigel at thewattdoctors.com<mailto:Dave.Weigel at thewattdoctors.com>> wrote:
Hi eQuest Group,

I was wondering if there is a quick way to determine how much of the projected energy use in a building is due to conditioning of ventilation air?  I have scoured through the eQuest reports and detailed simulation output but no luck (unless I'm missing something). I suppose I can run the simulation again with ventilation set to zero, but it would be great if it could be drawn straight from the simulation output.

Thanks!

Dave


David R. Weigel, PE
Managing Member
1189 Golden Circle SW,  Lilburn GA 30047
678-353-6394<tel:678-353-6394> office       901-619-1716<tel:901-619-1716> cell


_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>


________________________________
The contents of this email and any attachments to it contain confidential and/or legally privileged information from Zimmer Gunsul Frasca Architects LLP or its affiliates. If you are not the intended recipient, or an employee or agent responsible for delivering this message to the intended recipient, be aware that any disclosure, copying, distribution, or use of the information contained herein is strictly prohibited. If you received this transmission in error, please contact the sender and destroy the material in its entirety, whether in electronic or hard copy format.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130911/0f537171/attachment-0002.htm>


More information about the Equest-users mailing list