[Equest-users] Splitting a space in detailed mode
Robert Stephenson
rstephenson at veic.org
Fri Sep 20 05:55:46 PDT 2013
Hi Gerald,
It sounds like you are on the right track with copying the polygons. My advice would be to copy the original polygon twice, once for each of the new spaces, and then delete the irrelevant half from each of those new polygons to define the two new spaces. Leave your original space polygon in the model.
For the first new space, you reassign the original space you are splitting to the first of the new polygons. Reassign walls by Location (VX of space polygon), and they should automatically take on the length and height required. You will likely have to reposition windows and for interior walls redefine the Next To definition to the appropriate adjacent space. Some existing walls will need to be deleted, but you will rebuild them in the next step. Jumping around between the 2D and 3D views has been helpful for me when doing this type of thing in the past.
For the second space, create a new space within your Floor and set the polygon for this space to the second polygon you created above. If you use the same X, Y, and Z coordinates of the original space, everything should line up. You can then create new interior/exterior walls and associated objects as required. Copying them from other existing walls makes this easy, just reassign the Location (VX of space polygon).
This should avoid the error you highlighted in your message, as you are not actively editing a polygon used by any existing space when working with the two copies. Hope that was clearer than mud…
Robert Stephenson
Technical Energy Analyst
VEIC Evaluation, Measurement and Verification Services
Burlington, 05401
802 540 7809
www.veic.org<http://www.veic.org/>
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jeremy McClanathan
Sent: Thursday, September 19, 2013 5:57 PM
To: 'Gerard Hazel'; 'equest-users at lists.onebuilding.org'
Subject: Re: [Equest-users] Splitting a space in detailed mode
That error means you cannot delete a vertex while something depends on it. You can open the interior wall and temporarily reassign it to another polygon, delete the vertex, then reassign the interior wall to the appropriate polygon. Or, you could just delete the interior wall, then delete the vertex.
Jeremy
[cid:image001.png at 01CEB5DF.317838E0]
___________________________________________
Jeremy McClanathan, P.E., BEMP, HFDP, LEED® AP
[cid:image002.jpg at 01CEB5DF.317838E0]
19203 36th Avenue W, Suite 200, Lynnwood, WA 98036
P 425-672-1071 | F 425-778-8769
P Please consider the environment before printing this email.
From: Gerard Hazel [mailto:ghazel at meengineers.com]
Sent: Thursday, September 19, 2013 2:47 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Splitting a space in detailed mode
Hi All,
I am in detailed mode with a fairly complex model l in which I must now split an irregularly shaped space into two. I have researched the archives and have attempted to follow the guidance I found there by copying and modifying the polygon. The problem I am having is when I try to delete vertices in the original to form the new space, I get a message which says the selected vertex cannot be deleted because the interior walls would not be attached to a shape vertex. How do I reassign walls to the new polygon?
If anyone has experience with this I would really appreciate the help.
Thanks,
Gerry Hazel
Gerard Hazel
M&E Engineers, Inc.
908-526-5700 x14
This email message, including any attachments, is for the sole use of the intended recipient and may contain confidential, proprietary, and/or privileged information, as well as content subject to copyright and other intellectual laws. If you are not the intended recipient, you may not disclose, use, copy, or distribute the email message or its attachments. If you believe you have received this email message in error, please contact the sender by reply email, immediately delete this email and destroy copies.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130920/72edb90f/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 30439 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130920/72edb90f/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1232 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130920/72edb90f/attachment-0002.jpg>
More information about the Equest-users
mailing list