[Equest-users] HEAT-EIR-FT for heat pumps with water	cooled	condensers?
    Brian Fountain 
    bfountain at greensim.com
       
    Mon Apr 14 09:11:29 PDT 2014
    
    
  
Thank you all for the replies.  I did receive a definitive answer:
 
"Entering mixed air temperature to the indoor coil(s) and entering fluid
temperature for the water side."
 
Plus, I received the excellent guidance from Aaron pointing out the
differences in the "HP- " series part load curves which are normalized on
ARI conditions and the "GSHP/WLHP- " series part load curves which are
normalized on GSHP loop conditions and require modifications to the EIR and
capacity.  The "GSHP/WLHP- " are the defaults coming out of the wizard.
 
Cheers,
 
From: Anthony Hardman [mailto:anthony at greenengineer.com] 
Sent: Monday, April 14, 2014 12:01 PM
To: 'Brian Fountain'; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] HEAT-EIR-FT for heat pumps with water cooled
condensers?
 
Entering indoor wet bulb and entering (condenser) water temperature I
believe.
 
Anthony Hardman, PE, LEED AP BD+C
Senior Building Performance Analyst
The Green Engineer, Inc.
Sustainable Design Consulting
54 Junction Square Dr.
Concord, MA 01742
O: (978) 610-2801
C: (720) 840-7862
 
The Green Engineer, Inc. is a Certified B Corporation
 
From: Brian Fountain [mailto:bfountain at greensim.com] 
Sent: Sunday, April 13, 2014 1:21 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] HEAT-EIR-FT for heat pumps with water cooled
condensers?
 
I am modelling a building with distributed water loop heat pumps.  I am
looking at the electricity used for space heating (the compressor energy in
heating mode).   This depends on a part load curve HEAT-EIR-FT which is a
function of two temperatures.  Based on the DOE2 documentation, it is not
clear to me which two temperatures this curve is using to modify the
compressor energy for a water-cooled heat pump. 
 
For an air-cooled heat pump, the curve is a function of entering dry-bulb
temperature and outdoor dry-bulb temperature.  I want to know what the X and
Y values are for a water-cooled heat pump.
 
Can anyone provide any clarification on this?
 
Many thanks.
 
Brian