What happens when you do this? (I haven't tried it.)
- Set the fan schedule to "1" during occupied hours and "0" during unoccupied.
- Set Indoor Fan Mode to "Intermittent".
- Set Night Cycle Control to "Cycle on Any".
- Create custom hourly report tracking supply air flow rate and supply fan elec (kW) and look for lower kW during unoccupied hours.
If this is for ASHRAE 90.1, G3.1.2.4, I have been doing all of the above except keeping the Fan Mode as "Continuous".
Regards,
Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[cid:image008.jpg at 01CFC138.F1C347B0] [cid:image009.jpg at 01CFC138.F1C347B0]
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Urban, Eric
Sent: Tuesday, August 26, 2014 1:48 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Fan coil indoor fan mode
Does anyone know if it's possible to (or have a workaround to) run fan coil indoor fans as "Continuous" during occupied hours but "Intermittent" during unoccupied hours?
Thanks,
Eric Urban
Sustainability Analyst
Stantec
[Image removed by sender. Stantec]<http://www.stantec.com/>
Celebrating 60 years of community, creativity, and client relationships.
The content of this email is the confidential property of Stantec and should not be copied, modified, retransmitted, or used for any purpose except with Stantec's written authorization. If you are not the intended recipient, please delete all copies and notify us immediately.
? Please consider the environment before printing this email.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140826/c6b42d58/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.jpg
Type: image/jpeg
Size: 1517 bytes
Desc: image008.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140826/c6b42d58/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image009.jpg
Type: image/jpeg
Size: 1647 bytes
Desc: image009.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140826/c6b42d58/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image010.png
Type: image/png
Size: 3859 bytes
Desc: image010.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140826/c6b42d58/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image011.jpg
Type: image/jpeg
Size: 371 bytes
Desc: image011.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140826/c6b42d58/attachment-0002.jpg>
More information about the Equest-users
mailing list