[Equest-users] Belimo Valve PlugIn
Javed Iqbal
eee.javed at gmail.com
Tue Feb 11 07:08:00 PST 2014
Dear Bishop,
My demo run also shows similar savings numbers which i feel needs to be
validated before using it for code compliance submission.
Any suggestions???
On Tue, Feb 11, 2014 at 9:24 AM, Bishop, Bill <bbishop at pathfinder-ea.com>wrote:
> Thanks, Rohini and Javed.
>
> I installed the plugin but I also had the same problem as Rohini with no
> documentation. I tried the "Belimo-Pressure-Depen-5-10 psi" curve in a
> random model and the pump energy increased 103%. And that's just when I use
> it for variable speed pumps. The literature doesn't warn you not to apply
> to single-speed pumps for additional savings, but there's nothing stopping
> you from doing that in eQUEST.
>
> A PIV Plug-in Brochure/Flyer<https://www.belimo.us/ishop/cms/sh/news_events/plugin.html>mentions that "full documentation of the development of the Belimo pressure
> dependent pump performance curves is included along with the plug-in to
> make your models easily defensible to the most demanding audience". But I
> don't have the documentation (or I can't find it). If anybody has a copy of
> this documentation, please share as I would consider using it for pump
> energy savings in my models when I'm confident the savings are realistic.
>
>
>
> Thanks,
>
> Bill
>
>
>
> *William Bishop, PE, BEMP, BEAP, LEED AP **|** Pathfinder Engineers &
> Architects LLP*
>
> *Senior Energy Engineer*
>
> [image: webCertified_logo_colorRGB72DPI.jpg]
>
>
>
> 134 South Fitzhugh Street Rochester, NY 14608
>
> *T: (585) 698-1956* F: (585) 325-6005
>
> bbishop at pathfinder-ea.com <wbishop at pathfinder-ea.com>
> www.pathfinder-ea.com
>
> [image: earth for signature]Sustainability - the forest AND the trees.
>
>
>
>
>
> *From:* R B [mailto:slv3sat at gmail.com]
> *Sent:* Monday, February 10, 2014 2:48 PM
> *To:* Javed Iqbal; Bishop, Bill; eQUEST Users List
> *Subject:* Re: [Equest-users] Belimo Valve PlugIn
>
>
>
> Here is what I found out about the Belimo valve eQuest curves. They are
> pump power curves to be used for baseline and the eQuest default curves
> would be the proposed (chw/hw system which has a pressure independent
> valve). The attached has more information if you are interested.
>
> Thanks,
>
> -Rohini
>
>
>
> On Thu, Jan 30, 2014 at 11:25 AM, Javed Iqbal <eee.javed at gmail.com> wrote:
>
> Hi,
>
>
>
> Are you looking for this document? I also tried installing this plugin but
> found an installation error as "3.65 Data" folder doesn't exist. I've 3.64b
> installed on my laptop and this plugin supports 3.6X all version as per
> developer. Did you find this problem?
>
>
>
> Thanks for sharing.
>
>
>
> On Thu, Jan 30, 2014 at 2:04 AM, R B <slv3sat at gmail.com> wrote:
>
> Has anyone used the belimo plug in? On installation, it is supposed to
> show the eQuest instruction documentation, but unfortunately that is not
> happening on my computer. If any one has this sheet, can you please forward
> it to me (assuming it is a regular text or pdf file).
>
> Here is the link if anyone is interested.
> https://www.belimo.us/americas/sp_online.html
>
> Thanks,
>
> -Rohini
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
>
>
> --
>
>
>
>
>
> Javed Iqbal, LEED AP, CEA
>
> Sr. Energy Analyst
>
>
>
>
>
>
>
>
>
>
>
>
>
--
Javed Iqbal, LEED AP, CEA
Sr. Energy Analyst
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140211/28cc3377/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 3124 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140211/28cc3377/attachment-0002.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 4600 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140211/28cc3377/attachment-0002.png>
More information about the Equest-users
mailing list