[Equest-users] LEED and Seasonal operation / DHW heater	seasonal	operation
    James Hansen 
    JHANSEN at ghtltd.com
       
    Wed Jan 29 14:29:40 PST 2014
    
    
  
Recirculation set to 0.01 may be the problem?  Can't you force equipment
on/off via load management / scheduling?
 
Also, like Nick said, there shouldn't be an issue with unoccupied
periods for schools, but make sure whoever does your FTE calcs takes
that into consideration, and that all Water Efficiency calculations have
+/- 40 weeks per year in lieu of 52.
 
GHT Limited
James Hansen, PE, LEED AP, BEMP
Senior Associate
1110 N. Glebe Road, Suite 300
Arlington, VA 22201
703.243.1200 (main)
703.338.5754 (direct/cell)
www.ghtltd.com <http://www.ghtltd.com> 
 
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nick
Caton
Sent: Wednesday, January 29, 2014 5:24 PM
To: Nick Patsos; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] LEED and Seasonal operation / DHW heater
seasonal operation
 
1.      I don't think LEED precludes you from modeling a building being
unoccupied for a good chunk of the year (assuming baseline and proposed
have matching schedules), but I would anticipate this to raise some
flags without substantial explanation and backup.  Acquiring something
from the district/owner in writing to submit alongside regular
documentation to back up your scheduling might save you a headache
later.
2.      If there's no pump operation (verified by hourly reports) or
scheduled DHW demand, I think that only leaves the pilot light... ?
That would show up as misc. gas consumption by default, if occurring.
You might post your project to get a second set of eyes on the problem.
 
Hope that helps!
 
~Nick
 
 
 
NICK CATON, P.E.
SENIOR ENGINEER
 
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com 
 
From: equest-users-bounces at lists.onebuilding.org [
mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nick
Patsos
Sent: Wednesday, January 29, 2014 9:29 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] LEED and Seasonal operation / DHW heater
seasonal operation
 
Hi all,
 
I'm currently modelling a school building in eQuest for the LEED for
Schools 2009 certification. The school doesn't operate at all in the
summer season (closed) and so it isn't equipped with equipment for
cooling.
 
I have made schedules modelling this principle (not operating in
JUNE/JULY/AUGUST) at both proposed and baseline scenarios but I'm
concerned if it is mandatory or not to model a full year's operation
under LEED. In the months of operation, I have modelled both
cooling/heating as it is mandatory.
 
A second question is how to make the DHW heater not to operate at the
summer months. Having tried everything and after doublechecking that
there is no DHW demand from the annual schedule for the summer months,
the result is that the DHW loop and pump show no use for these months
(seen at the simulation output) but still the DHW heater is operating
consuming significant gas for an unknown reason. Loop is set to demand
operation and recirculation set at 0.01.
 
Any help highly appreciated. Thanks in advance!
 
Nikos Patsos
Mechanical Engineer
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140129/3b294f50/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140129/3b294f50/attachment-0002.jpeg>
    
    
More information about the Equest-users
mailing list