[Equest-users] Baseline system for tenant improvement
Chris Baker
CBaker at cci-alliance.com
Mon Jun 16 12:24:25 PDT 2014
Steve,
ASHRAE 90.1 Appendix G talks about that a little bit.
See sheet 4 of 47 - "Trade-Off limits"
http://web.cecs.pdx.edu/~sailor/CoursePages/ME422_Spr09/ASHRAE90_1Appendix_G.pdf
Basically, it is possible but very specific guidelines must be met - as the document talks about.
Also, if you have, for example, heating and air-side systems serving both the newly-renovated area and the other parts of the building the energy results of the model could potentially be much better (more energy efficient) than it actually is.
This means that the results of the energy model have a possibility of being misconstrued and skewed somewhat which ASHRAE specifically frowns upon because it can be dishonest and not reflective of the ACTUAL energy use of the building. It also means the energy cost comparison is undermined by the fact that the ACTUAL cost savings could be much lower than the client is expecting and that could cause some issues.
Sheet 3 of 47- "Include All Energy Components" talks about this.
But if the minimum requirements are met, you have an argument and a direct reference in ASHRAE at your defense.
I've never heard of someone modeling only a portion of a larger building but apparently ASHRAE sais it is possible. But to do it accurately the portion of the building being modeled would need its own air-side system, it's own heating system, etc... It would be the only way to accurately model the building.
I would think you would also need to calculate energy cost for the overall building before doing any kind of realistic or accurate cost comparison for the client.
Especially since the model would only reflect cost savings for the renovated portion, not the entire building.
I'd be interested to see what others think about this.
Chris Baker
CCI CAD Drafter
-----Original Message-----
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Steve Jacobs
Sent: Monday, June 16, 2014 8:12 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Baseline system for tenant improvement
I asked this question last week but it sounds like some of the messages weren't getting through.
If a project modeling scope is 20,000 SF of a larger building, does the baseline system need to be based on the whole building area or just the
20,000 SF?
Thanks,
Steve
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
CCI-Alliance Confidentiality notice: This message is intended only for the person to whom addressed in the text above and may contain privileged or confidential information. If you are not that person, any use of this message is prohibited. We request that you notify us by reply to this message, and then delete all copies of this message including any contained in your reply. Thank you.
More information about the Equest-users
mailing list