Without seeing your file it is difficult to find what the problem is that you are having. You must specify a reheat delta T in order for the reheat to turn on. Usually 30 degrees is a good starting point. This is in detailed mode.
If you are still confused, please attach your .pd2. & .inp files for our review.
Pasha
Ph: 308-763-1593
> On Jun 16, 2014, at 2:22 PM, Morteza Kasmai <morteza.kasmai at gmail.com> wrote:
>
> Dear eQUEST experts,
>
> Could you please respond to my question in email the below?
>
> Regards,
> Morteza
>
>
> ---------- Forwarded message ----------
> From: Morteza Kasmai <morteza.kasmai at gmail.com>
> To: "equest-users at lists.onebuilding.org" <equest-users at lists.onebuilding.org>
> Cc:
> Date: Fri, 13 Jun 2014 13:31:40 -0400
> Subject: How to add Re-Heat Coil to a RTU
> Hello all,
>
> My question regards adding a Re-Heat Coil to a RTU system in detailed data edit mode. The system has heating capacity and re-heat coil capacity, but I cannot find any place to input this data at the system level.
>
> Thank you for your help,
> Morteza
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140616/70f39c2c/attachment.htm>
More information about the Equest-users
mailing list