[Equest-users] how to model steam absorption chiller in eQUEST
John Aulbach
jra_sac at yahoo.com
Sun May 11 20:46:24 PDT 2014
Aaron:
Size the pump for the btus the chiller will require in hot water load, then set the pump kW to Zero. Pump will still work ,just not use any energy. You will need a steam boiler connected to the chiller, with probably a 100% efficiency. In that way, you are essentially firing the chiller with steam.
John R. Aulbach, PE
________________________________
From: Aaron <565520032 at qq.com>
To: equest-users <equest-users at lists.onebuilding.org>
Sent: Sunday, May 11, 2014 8:33 PM
Subject: [Equest-users] how to model steam absorption chiller in eQUEST
Hi guys
I'm modelling a steam absorption chiller, but seems not easy. I've set the chiller as below. I set heating source as Hot water loop, because seems steam is not available for absorption chiller.
I set steam meter for steam source,
but error appears after running the model saying absorption chiller must have a pump for absorption steam loop as below.
please, could anyone give some guide on this problem for me?
thanks
Aaron
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140511/c1bfaa31/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 106552 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140511/c1bfaa31/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 14271 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140511/c1bfaa31/attachment-0001.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 27650 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140511/c1bfaa31/attachment-0002.jpeg>
More information about the Equest-users
mailing list