[Equest-users] Space by Space LPD requirements for 90.1 modeling
Cam Fitzgerald
cam at energyopportunities.com
Fri May 23 05:29:41 PDT 2014
Dear Javid,
You are right to question this review comment. Interior lighting is tradable
when using energy simulations not the prescriptive 90.1 requirements. I
suggest you send an inquiry to the review team requesting confirmation of
the requirement and further explanation. You should explain your
understanding of the Appendix G requirements and briefly explain how the
lighting is modeled in the baseline and proposed case. Clarifying the issue
before you make any changes to the model and resubmit could save a lot of
headache (and time). Good luck!
Cam Fitzgerald
Energy Opportunities/a 7group company
1200 E Camping Area Rd, Wellsville, PA 17365
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On
Behalf Of Javed Iqbal
Sent: Friday, May 23, 2014 7:53 AM
To: equest-users
Subject: [Equest-users] Space by Space LPD requirements for 90.1 modeling
Dear All,
Recently i have received a comment from design team peer reviewer on
applicability of space by space lighting power density for 90.1 appendix G
compliance modeling for manufacturing facility and given as follows:
"Space by Space" method can only be used if the actual proposed design meets
the space by space requirements for each included space type.
I found similar discussion happened on 23/5/12- Building Area Method 90.1
(great insight from Nick) but didn't noticed any such requirements like
mentioned above. I am clueless on this and can't even verify if this is a
valid comment.
I would appreciate if someone could guide me on this.
Thanks in advance,
--
Javed Iqbal, LEED AP, CEA
Sr. Energy Analyst
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140523/768ba66c/attachment.htm>
More information about the Equest-users
mailing list