[Equest-users] PIU system central heat coil ouput
David Reddy
david at 360-analytics.com
Fri Oct 17 14:12:18 PDT 2014
Hi Erik,
Yes, I should have mentioned that I tried that too. That is typically
what I do, but I thought perhaps defining a heat source with a small
amount of capacity would be a reasonable way to alleviate the "free"
heat energy I appear to be getting...
Attached is a quick and dirty wizard model that illustrates the issue
(you will need to download .bin file or change to something
comparable). This is representative of the configuration I was going
for except air-cooled DX.
David
On 10/17/2014 2:00 PM, Erik Kolderup wrote:
> David,
>
> Have you tried setting the HEAT-SET-T (Hot Deck Max Leaving Temp) to
> no value (i.e. Restore Default)? I think that any value for that
> keyword enables heating at the AHU level.
>
> -Erik
>
> *Erik Kolderup, PE, LEED AP*
> erik at kolderupconsulting.com <mailto:erik at kolderupconsulting.com>|
> 415.531.5198 | www.kolderupconsulting.com
> <http://www.kolderupconsulting.com>
>
> On Fri, Oct 17, 2014 at 1:29 PM, David Reddy <david at 360-analytics.com
> <mailto:david at 360-analytics.com>> wrote:
>
> Hi all,
> I am modeling a PIU system w/ a water-cooled DX coil and series
> electric FPBs; no central or preheat heating coils. Using eQ v3.64
>
> SV-A report indicates heating capacity for system is 0.
>
> Despite this configuration, hourly reports of for SYSTEM, 'Total
> central heat coil output (Btu/hr)' indicates there is varying
> amount of central heat energy output in the first 1-2 and in some
> cases, the last 2-3 hours of many days in heating months (location
> Seattle, WA). This is also confirmed by looking at the difference
> in energy reported between SS-A Heating and SS-B Zone Heating. It
> is not necessarily a trivial amount of energy, ~25% of total.
>
> Have others observed this before, and if so, found a way to fix this?
>
> Can't say I've tried everything I can think of, but this is what I
> have tried:
>
> A) Set HEAT-SOURCE = "ELECTRIC" and use a very small capacity both
> -1 or -1000
> B) A + setting HEAT-CONTROL = "CONSTANT"
> C) B + set HEAT-SET-T various values, including minimum (50F)
> D) Setting HEATING-SCHEDULE to something that locks out heating.
> This works, but also locks out zone heating, so not a viable solution
>
> Thanks in advance for any input.
> -David
>
>
> --
>
> David Reddy
>
> *360 Analytics*
> Building Energy Analysis Consultants
> mail: 9750 3rd Ave NE, Suite 405, Seattle, WA 98115
> office: 206.557.4732 x 201 <tel:206.557.4732%20x%20201>
> cell: 206.406.9856 <tel:206.406.9856>
> web: www.360-Analytics.com <http://www.360-Analytics.com>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
> <mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20141017/a3f5efe4/attachment-0001.htm>