[Equest-users] What do reports report?
R B
slv3sat at gmail.com
Tue Feb 10 12:06:29 PST 2015
LS-A is for the space or whole building depending on which cooling load
value you are looking at, without the systems. LS-D is for the whole
building. SS-D is for all the systems together. SS-A is for a particular
system. SS-D will include the outdoor air, and the thermostat setting you
are using. If you have only one system in the building, SS-D and SS-A will
be same.
On Tue, Feb 10, 2015 at 1:47 PM, Charles Hoes <charles_hoes at hoes-eng.com>
wrote:
> I have been attempting to successfully use eQuest for the past year or so
> and am finding it to be an excruciatingly frustrating experience. It is
> definitely a "quirky" program.
>
> My latest confusion has to do with the difference between the LS-A, SS-A
> and SS-D reports. The documentation indicates that you need to go to SS-A
> to results that account for time varying air temperatures. SS-A reports
> are not described in the Detailed Simulation Reports Summary, nor anywhere
> else that I can find.
>
> LS-A Space Peak Loads reports:
>
> Cooling peak = 35.070 KBTU/hr; Heating Peak = -20.826 KBTU/hr.
>
> SS-A System Loads Summary reports: (not included in Detailed Simulation
> Reports Summary documentation)
>
> Cooling maximum = 2.684 KBTU/hr; Heating Maximum = -4.275 KBTU/hr
>
> SS-D Building HVAC Load Summary reports: (not included in Detailed
> Simulation Reports Summary documentation)
>
> Cooling maximum = 24.81 KBTU/hr; Heating maximum = -28.14 KBTU/hr
>
> I am wondering what these results could possibly mean. The order of
> magnitude difference between the LS-A and SS-A reports baffles me. I MIGHT
> be able to understand it for cooling if the SS-A results were ten times as
> high, but I don't understand how the heating could be double. These values
> don't seem to make sense, but since there is no description of the reports
> there is no way to tell.
>
> The SS-D report seems to make some sort of sense in relation to the LS-A
> report if the LS-A report is giving "instantaneous" results as if the
> building were at a steady state condition and the SS-D report includes the
> impacts of thermal mass and things like that. However, since there is no
> documentation on this I am must guessing.
>
> I am of course being interested in sizing a heating and cooling system for
> the building. Given these different and unexplained differences in the
> reports I am finding that to be difficult to do.
>
> Can anyone explain what these reports are telling me and how I might best
> use them as part of the design process? Right now I just have to pick one
> that "feels" good - but that isn't a very satisfying approach.
>
> Thanks
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150210/702645cc/attachment.htm>
More information about the Equest-users
mailing list