[Equest-users] What do reports report?

bfountain at greensim.com bfountain at greensim.com
Tue Feb 10 12:55:12 PST 2015


>From the Detailed Simulation Reports Summary (a searchable .pdf accessible
from the Help->Tutorials and References menu):







 

 



 

Keep in mind, LOADS reports LS- do not include outdoor air for ventilation -
that is added at the SYSTEM level.

 

 

-----Original Message-----
From: Charles Hoes [mailto:charles_hoes at hoes-eng.com] 
Sent: February-10-15 3:35 PM
To: bfountain at greensim.com
Subject: Re: [Equest-users] What do reports report?

 

Thanks.  I keep getting this advice to look at the detailed report
descriptions.  However, as I mentioned in my email, those descriptions do
not include the reports that I am referring to (or if they are listed, they
are out of order because I can't find them).

 

I'll check out the tutorial on DOE-2 again.  I have done this several times
and found no useful information, but I'll keep trying.

 

Charlie

 

 

On 2/10/2015 12:10 PM,  <mailto:bfountain at greensim.com>
bfountain at greensim.com wrote:

> Have a look at the description of the reports under Help->Tutorials and
Reference->Detailed Report Description.

> 

> Also, review the tutorial to understand the difference between LOADS and
SYSTEMS runs in DOE-2.

> 

> 

> -----Original Message-----

> From: Charles Hoes < <mailto:charles_hoes at hoes-eng.com>
charles_hoes at hoes-eng.com>

> Sender: "Equest-users" <
<mailto:equest-users-bounces at lists.onebuilding.org>
equest-users-bounces at lists.onebuilding.org>

> Date: Tue, 10 Feb 2015 11:47:02

> To: < <mailto:equest-users at lists.onebuilding.org>
equest-users at lists.onebuilding.org>

> Subject: [Equest-users] What do reports report?

> 

> I have been attempting to successfully use eQuest for the past year or 

> so and am finding it to be an excruciatingly frustrating experience.  

> It is definitely a "quirky" program.

> 

> My latest confusion has to do with the difference between the LS-A, 

> SS-A and SS-D reports.  The documentation indicates that you need to 

> go to SS-A to results that account for time varying air temperatures.  

> SS-A reports are not described in the Detailed Simulation Reports 

> Summary, nor anywhere else that I can find.

> 

> LS-A Space Peak Loads reports:

> 

> Cooling peak = 35.070 KBTU/hr; Heating Peak = -20.826 KBTU/hr.

> 

> SS-A System Loads Summary reports: (not included in Detailed 

> Simulation Reports Summary documentation)

> 

> Cooling maximum = 2.684 KBTU/hr; Heating Maximum = -4.275 KBTU/hr

> 

> SS-D Building HVAC Load Summary reports: (not included in Detailed 

> Simulation Reports Summary documentation)

> 

> Cooling maximum = 24.81 KBTU/hr; Heating maximum = -28.14 KBTU/hr

> 

> I am wondering what these results could possibly mean.  The order of 

> magnitude difference between the LS-A and SS-A reports baffles me. I 

> MIGHT be able to understand it for cooling if the SS-A results were 

> ten times as high, but I don't understand how the heating could be double.

> These values don't seem to make sense, but since there is no 

> description of the reports there is no way to tell.

> 

> The SS-D report seems to make some sort of sense in relation to the 

> LS-A report if the LS-A report is giving "instantaneous" results as if 

> the building were at a steady state condition and the SS-D report 

> includes the impacts of thermal mass and things like that.  However, 

> since there is no documentation on this I am must guessing.

> 

> I am of course being interested in sizing a heating and cooling system 

> for the building.  Given these different and unexplained differences 

> in the reports I am finding that to be difficult to do.

> 

> Can anyone explain what these reports are telling me and how I might 

> best use them as part of the design process?  Right now I just have to 

> pick one that "feels" good - but that isn't a very satisfying approach.

> 

> Thanks

> _______________________________________________

> Equest-users mailing list

>  <http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org>
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org

> To unsubscribe from this mailing list send  a blank message to 

>  <mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150210/e1e32859/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 100296 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150210/e1e32859/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 105704 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150210/e1e32859/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 114034 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150210/e1e32859/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 13717 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150210/e1e32859/attachment.jpeg>


More information about the Equest-users mailing list