[Equest-users] eQUEST Transformer Loss - incorrect error if < 1
    bfountain at greensim.com 
    bfountain at greensim.com
       
    Mon Jan 19 07:46:59 PST 2015
    
    
  
The transformer loss in eQUEST should be the fraction of output power lost
at full load.  It should be in the order of 1 to 3% so an input of 0.02 for
example.  However the range checking in eQUEST is looking for a value
greater than 1 (in the range of 1  1.5).  A value of 1 does in fact double
your electrical usage (with ½ going to Pumps and Aux for the transformer
loss) so the range checking is in error.
 
 
Is there a way to access and change the error checking values?
 
Thank you.
 