[Equest-users] eQUEST Transformer Loss - incorrect error if < 1
Nicholas Caton
ncaton at catonenergy.com
Mon Jan 19 12:49:31 PST 2015
Hi Brian,
I went deep into this rabbit hole some years back, rolling my own custom
curves along the way to quantify savings for premium efficiency
transformers... I can look to my notes/records later, but don't recall any
such "nonstarter" errors along the way.
It might be productive to transpose your efforts into a dummy model to
explore whether the same error occurs using equest 3.63... Something may
have changed since then which you could be the first to stumble into!
On Jan 19, 2015 10:10 AM, <bfountain at greensim.com> wrote:
> The transformer loss in eQUEST should be the fraction of output power lost
> at full load. It should be in the order of 1 to 3% so an input of 0.02 for
> example. However the range checking in eQUEST is looking for a value
> greater than 1 (in the range of 1 – 1.5). A value of 1 does in fact double
> your electrical usage (with ½ going to Pumps and Aux for the transformer
> loss) so the range checking is in error.
>
>
>
>
>
> Is there a way to access and change the error checking values?
>
>
>
> Thank you.
>
>
>
> Brian
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150119/8101db0d/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 33658 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150119/8101db0d/attachment-0001.png>
More information about the Equest-users
mailing list