[Equest-users] Ventilation
    David Griffin II 
    DGriffin at archnexus.com
       
    Fri Jan 30 15:38:57 PST 2015
    
    
  
Farid,
I have run into issues in the past with trying to specify two or more different types of airflow (i.e. CFM/Area, CFM, ACH) in the same model. Therefore, I use some BDL scripting which combines my flow rate types into one category similar to the script below which assigns flow rate based on the "C-ACTIVITY-DESC" of the space.
if (#LR("SPACE","C-ACTIVITY-DESC")=="Flor")
then (#LR("SPACE","HEIGHT")*3)/#LR("SPACE","AREA")/60
else
((#LR("SPACE","NUMBER-OF-PEOPLE"))*17)/(#LR("SPACE","AREA"))
endif
/*([Space Height]*[OA ACH])/[Conversion]
/*or
/*([# of people in space]*[Typical CFM/Person for office space])/[Space Area]
Hopefully this helps.
Sincerely,
David Griffin, BEMP
Senior Energy Analyst
ARCHITECTURAL
NEXUS
2505 E Parleys Way
Salt Lake City, UT 84109
Office  801.924.5000
Direct  801.924.5028
archnexus.com<http://www.archnexus.com/> | blog<http://www.nexusfocus.com/> | facebook<https://www.facebook.com/pages/Architectural-Nexus/179588705397563> | youtube<http://www.youtube.com/channel/UCYRPWKF-yp-AUiI8ia2XfKw>
From: Berty, David [mailto:David.Berty at covance.com]
Sent: Friday, January 30, 2015 6:44 AM
To: Sami, Vikram; Farid Pour; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Ventilation
I agree, input airflow rates as ACH instead of cfm/person or any other by changing the units in the wizard (drop-down box option). This is designed for and works well for process-driven ventilation rates.
David Berty, P.E.
Utility/Mechanical Engineer
T: +011.317.467.3294
M: +011.317.448.0482
Covance - Early Development
671 S. Meridian, Greenfield, IN 46140-5006
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Sami, Vikram
Sent: Thursday, January 29, 2015 9:38 PM
To: Farid Pour; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Ventilation
It will be high. 16ACH with a 15ft ceiling is massive - that's 4cfm/ft2.
You do have the option of inputting the ventilation rates as ACH and not cfm/person - which is how I would recommend doing it. The reason being - if it's a lab, you are likely ventilating at a rate or schedule that's not tied to the human occupancy schedule.
Vikram Sami
BEMP, LEED BD+C
Associate Partner
ZGF ARCHITECTS LLP
T 206.521.3509 E vikram.sami at zgf.com<mailto:vikram.sami at zgf.com>
925 Fourth Avenue, Suite 2400
Seattle, WA 98104
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Farid Pour
Sent: Thursday, January 29, 2015 12:52 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Ventilation
Hi
I am trying to model an existing Lab buildng with 16ACH actual ventilation rate. the height of the floor to ceiling is 15ft, the area is 35556 SF and about 100 people are working in the building.
How can I calculate CFM per person. The numbers I am getting is really high and is not even close to ahrae 62.1
Here is what I did for calculation
CFM/person = 16 (ach) x 35556 SF x 15ft / 60 / 100person
[cid:image001.png at 01D03CA4.A39F17C0]
ZGF Email Disclaimer<https://www.zgf.com/ZGF_Email_Disclaimer.html>
________________________________
Confidentiality Notice: In accordance with Covance's Data Classification Policy, this email, including attachment(s), is classified as Confidential or Highly Confidential. This e-mail transmission may contain confidential or legally privileged information that is intended only for the individual or entity named in the e-mail address. If you are not the intended recipient, you are hereby notified that any disclosure, copying, distribution, or dissemination of the content of this e-mail is strictly prohibited.
If you have received this e-mail transmission in error or this email is not intended for you, please delete or destroy all copies of this message in your possession and inform the sender. Thank you.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150130/87b767fa/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 7392 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150130/87b767fa/attachment.png>
    
    
More information about the Equest-users
mailing list