[Equest-users] error msg: loop - no primary heating equipment attached
Nathan Miller
nathanm at rushingco.com
Thu Jul 16 06:32:26 PDT 2015
If Circulation Loop 5 is attached to the primary heating loop as its source of heat, then I believe you need to designate the Loop Subtype as “Secondary”. See Screen Shot:
[cid:image001.png at 01D0BFAA.4F7AAE50]
Nathan Miller, PE, LEED AP BD+C – Mechanical Engineer/Senior Energy Analyst
RUSHING | D 206-788-4577 | O 206-285-7100
www.rushingco.com<http://www.rushingco.com/>
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Pranita Kothuru Komirishetty
Sent: Thursday, July 16, 2015 9:27 AM
To: equest-users
Subject: [Equest-users] error msg: loop - no primary heating equipment attached
Good Morning -
I am working on a 65 story building in eQuest 3.64. The building is cooled by Standard VAV units (primary cooling equipement is chillers) heated by perimeter baseboards (steam boilers).
The first 6 floors of the building have perimeter induction units with no re-heat. For this I have created a different loop (linked this to the primary heating loop). This loop is called the Circulation Loop 5 in my model. I assign this loop to the baseboard loop in the air side HVAC parameters.
When I run the simulation I get the following error:
***ERROR***********************************************************************
Loop: Circulation Loop 5 has no attached primary
heating equipment.
I could not find anything in the archives directly to tackle this issue. Not an expert in HVAC and hence need your advise.
snapshot of loop window:
[Inline image 1]
Thanks in advance.
--
- Pranita
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150716/f8d0ac88/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 65545 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150716/f8d0ac88/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 122868 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150716/f8d0ac88/attachment-0001.png>
More information about the Equest-users
mailing list