[Equest-users] Indoor fan separation at ARI
Maria Karpman
maria.karpman at karpmanconsulting.net
Thu Jun 11 08:26:37 PDT 2015
Omar,
“2” after SEER and HSPF means squared – I did not notice that formatting got messed up when I copied from 90.1. Here it is again:
On a separate note, 248 CFM design flow rate for the baseline HVAC system seems unrealistically low. I would double check that you are applying G3.1.1 correctly (For systems 1, 2, 3, and 4, each thermal block shall be modeled with its own HVAC system. For systems 5, 6, 7, and 8, each floor shall be modeled with a separate HVAC system.)
Good luck,
Maria
--
Maria Karpman LEED AP, BEMP, CEM
________________
Karpman Consulting
<http://www.karpmanconsulting.net/> www.karpmanconsulting.net
Phone 860.430.1909
41C New London Turnpike
Glastonbury, CT 06033
From: Jones, Christopher [mailto:Christopher.r.Jones at wspgroup.com]
Sent: Thursday, June 11, 2015 10:28 AM
To: Elizabeth Gillmor; Omar ElRawy
Cc: Maria Karpman; equest
Subject: RE: [Equest-users] Indoor fan separation at ARI
Hi Elizabeth,
I am looking at the EMITUsersGuide. The input dialog shown on page 12 asks for the Main Supply Fan Power and the Return Fan Power. I assume it is asking for the fan power at design conditions – bhp/motor efficiency from the fan curve?
cid:image003.png at 01D09C46.E75BA0D0
Christopher Jones, P.Eng.
Senior Engineer
WSP Canada Inc.
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4
T +1 416-644-4226
F +1 416-487-9766
C +1 416-697-0065
<http://www.wspgroup.com/> www.wspgroup.com
From: Elizabeth Gillmor [ <mailto:elizabeth at energetics-eng.com> mailto:elizabeth at energetics-eng.com]
Sent: Thursday, June 11, 2015 10:15 AM
To: Omar ElRawy
Cc: Maria Karpman; Jones, Christopher; equest
Subject: Re: [Equest-users] Indoor fan separation at ARI
Sorry for any confusion, I was just copying/pasting my LEED response for a system Type 5. Yes, you would follow G3.1.2.9 with the appropriate numbers for system types 3-4.
LEED refers you to the EMIT user guide for these formulas, you can reference that:
http://www.rmi.org/Content/Files/EMITUsersGuide.pdf
Elizabeth Gillmor PE, LC, LEED AP
e n e r g e t i c s consulting engineers, llc
<http://energetics-eng.com> energetics-eng.com
c 303.619.0091
On Thu, Jun 11, 2015 at 6:23 AM, Omar ElRawy <omaroelrawy at gmail.com> wrote:
Dear all,
Thanks William Bishop, Elizabeth Gillmor, Yongqingzhao, and Maria Karpman, this is a lot of helpful data.
I think Maria did brief the whole subject, but I just need to ask few questions that will help in well documenting this point to the LEED reviewer:
1. Where can I find these official formulas so that I can refer to and attach to my reply please?
2. What is the difference between SEER and SEER2, and HSPF and HSPF2?
Concerning fan power, I'am referring to ASHRAE 90.1 2007 section 3.1.2.9 to find the following:
bhp = CFMs x 0.00094 + A ----- (where I'am considering my auto-sized eQuest CFM for this value)
Pfan (Watts) = bhp × 746 / Fan Motor Efficiency (For systems 3 through 8)
So I'am stopping at both equations to find myself confused with Elizabeth's equations (KW/cfm = bhp/0.746*Fan Motor Efficiency, and bhp=CFM x 0.0013+A)
For example, my system is 248 CFM, as per section 3.1.2.9, my calculations will be as follows:
* bhp=248x0.00094+0 = 0.23312
* Pfan = (0.23312x746)/0.825 = 210.79 W
* W/CFM = 210.79/248 = 0.8499 W/CFM
I wonder if Elizabeth is using a different 90.1 version, or I'am just confused at the 3.1.2.9 interpretation?
Thanks for consideration,
Omar ElRawy, LEED AP BD+C
LEED Project Manager
EA Sustainable Building Consultants
<http://www.ea-buildingconsultants.com/> http://www.ea-buildingconsultants.com
On Wed, Jun 10, 2015 at 4:10 PM, Maria Karpman <maria.karpman at karpmanconsulting.net> wrote:
Note that 90.1 2013 finally supplied the “official” formulas for extracting fan power from EER, SEER, COP47, and HSPF ratings. The resulting EIR is slighting different compared to the eQUEST formulas discussed below that many of us have been using – for example, the ASHRAE equations account for system capacity, resulting in varying EIR depending on system size.
For Baseline HVAC Systems 1,
2, 3, 4, 5, and 6, calculate the minimum COPnfcooling and
COPnfheating using the equation for the applicable performance
rating as indicated in Tables 6.8.1-1 through 6.8.1-4.
Where a full- and part-load efficiency rating is provided in
Tables 6.8.1-1 through 6.8.1-4, the full-load equation below
shall be used:
COPnfcooling = 7.84E-8 × EER × Q + 0.338 × EER
COPnfcooling = –0.0076 × SEER2 + 0.3796 × SEER
COPnfheating = 1.48E-7 × COP47 × Q + 1.062 × COP47
(applies to heat-pump heating efficiency only)
COPnfheating = –0.0296 × HSPF2 + 0.7134 × HSPF
where COPnfcooling and COPnfheating are the packaged HVAC
equipment cooling and heating energy efficiency, respectively,
to be used in the baseline building, which excludes
supply fan power, and Q is the AHRI-rated cooling capacity
in Btu/h.
EER, SEER, COP, and HSPF shall be at AHRI test conditions.
Fan energy shall be modeled separately according to
Section G3.1.2.10.
--
Maria Karpman LEED AP, BEMP, CEM
________________
Karpman Consulting
<http://www.karpmanconsulting.net/> www.karpmanconsulting.net
Phone <tel:860.430.1909> 860.430.1909
41C New London Turnpike
Glastonbury, CT 06033
From: Equest-users [mailto: <mailto:equest-users-bounces at lists.onebuilding.org> equest-users-bounces at lists.onebuilding.org] On Behalf Of Elizabeth Gillmor
Sent: Tuesday, June 09, 2015 11:32 AM
To: Jones, Christopher
Cc: equest
Subject: Re: [Equest-users] Indoor fan separation at ARI
Chris you are right, the unit labels should have been W/cfm not kW. Thanks for the catch!
Inline image 2
Elizabeth Gillmor PE, LC, LEED AP
e n e r g e t i c s consulting engineers, llc
<http://energetics-eng.com> energetics-eng.com
c <tel:303.619.0091> 303.619.0091
On Tue, Jun 9, 2015 at 8:49 AM, Jones, Christopher <Christopher.r.Jones at wspgroup.com> wrote:
Just checking but 0.365 kW/cfm seems pretty high. That is 356 W/cfm. The DOE2.2 default is 0.0006 kW/cfm, 0.6 W/cfm for the PSZ system
cid:image003.png at 01D09C46.E75BA0D0
Christopher Jones, P.Eng.
Senior Engineer
WSP Canada Inc.
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4
T <tel:%2B1%20416-644-4226> +1 416-644-4226
F <tel:%2B1%20416-487-9766> +1 416-487-9766
C <tel:%2B1%20416-697-0065> +1 416-697-0065
<http://www.wspgroup.com/> www.wspgroup.com
From: Equest-users [mailto: <mailto:equest-users-bounces at lists.onebuilding.org> equest-users-bounces at lists.onebuilding.org] On Behalf Of Elizabeth Gillmor
Sent: Tuesday, June 09, 2015 10:09 AM
To: Omar ElRawy
Cc: equest
Subject: Re: [Equest-users] Indoor fan separation at ARI
I seem to get this comment frequently so I have it all typed out as a stock LEED comment response. The advice you received is correct. You can use the following formulas for fan power and EIR:
kW/cfm = BHP / 0.746 * Fan Motor Efficiency (<----from Appendix G)
BHP = CFM * 0.0013 + Pressure Drop Adjustment
The baseline EIR is then calculated with fan energy modeled separately, using the following formula (same as what eQuest uses in Wizard mode):
Inline image 1
Where ARI Fan Power = fan power at rated ARI conditions (W/Btuh), and CAP = total cooling capacity (Btuh). At rated ARI conditions, the supply fan is rated at 0.365 kW/cfm and 400 cfm/ton, such that:
Inline image 2
When normalizing the cooling capacity, the formula is:
Inline image 3
When applied to a baseline EER=9.5, the resulting EIR=0.3051. The eQuest wizard will also do this for you correctly, but usually at LEED submittal time we are all well past the wizard phase, so the formulas above are handy to have.
Good luck!
Elizabeth
Elizabeth Gillmor PE, LC, LEED AP
e n e r g e t i c s consulting engineers, llc
<http://energetics-eng.com> energetics-eng.com
c <tel:303.619.0091> 303.619.0091
On Tue, Jun 9, 2015 at 3:26 AM, Omar ElRawy <omaroelrawy at gmail.com> wrote:
Dear all,
I've got the following reply for a psz system in the baseline case during preliminary LEED design submittal:
"Note that section G3.1.2.1 requires that where efficiency ratings, such as EER and COP, include fan energy, the descriptor shall be broken down into its components so that supply fan energy can be modeled separately. Because the efficiency ratings are calculated at ARI-rated conditions, the fans should also be broken out at ARI-rated conditions. Most simulation software programs have the capability to perform this step automatically. Provide documentation showing that this calculation has been performed by the software automatically or provide calculations consistent with the ASHRAE 90.1-2007 User’s Manual showing that the calculation has been performed at ARI-rated conditions."
What I did is that I referred to eQuest library, and documented the following paragraph to the reviewer:
"COOLING-EIR:
The Electric Input Ratio (EIR), or 1/(Coefficient of Performance), for the cooling unit at ARI rated conditions..... This EIR is at ARI rated conditions, i.e., without correction for different temperature or part load. Note: If you include fan electric energy consumption in your value of COOLING-EIR, then you should set SUPPLY-KW/FLOW to zero. Otherwise, the supply fan electrical energy will be double counted........ Imbedding the fan energy into the COOLING-EIR is valid only if the fan is constant volume and INDOOR-FAN-MODE = INTERMITTENT; i.e. the fan cycles on/off with the compressor. If the fan runs continuously during occupied hours, or the fan is variable volume, then the fan energy cannot be included in the COOLING-EIR (or HEATING-EIR)."
And I did set fan kw/cfm to zero, intermittent, and constant volume, but I've got the SV-A report reporting zero kw power demand, and zero fan (kw) for the system and its zones.
Then I got an advice stating that:
"You should do what the reviewer mentions, divide the indoor fan from the efficiency rating at ARI-rated conditions and model it separately; this way you will be able to report the appropriate fan power"
My question is: where do I separately input the indoor fan power (kw), and what value should it be?, knowing that this is a baseline case that do not refer to an actual design.
Thanks,
Omar ElRawy, LEED AP BD+C
LEED Project Manager
EA Sustainable Building Consultants
<http://www.ea-buildingconsultants.com/> http://www.ea-buildingconsultants.com
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
_____
You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP’s electronic communications policy, please consult our Anti-Spam Commitment <http://www.wspgroup.com/casl> www.wspgroup.com/casl. For any concern or if you believe you should not be receiving this message, please forward this message to us at <mailto:caslcompliance at wspgroup.com> caslcompliance at wspgroup.com so that we can promptly address your request. This message is intended only for the use of the individual or entity to which it is addressed, and may contain information which is privileged, confidential, proprietary or exempt from disclosure under applicable law. If you are not the intended recipient or the person responsible for delivering the message to the intended recipient, you are strictly prohibited from disclosing, distributing, copying or in any way using this message. If you have received this communication in error, please notify the sender, and destroy and delete any copies you may have received.
WSP provides professional land surveying services through the following entities: WSP Surveys (AB) Limited Partnership and WSP Surveys (BC) Limited Partnership
_____
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2014.0.4800 / Virus Database: 4311/9974 - Release Date: 06/08/15
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
_____
You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP’s electronic communications policy, please consult our Anti-Spam Commitment www.wspgroup.com/casl. For any concern or if you believe you should not be receiving this message, please forward this message to us at <mailto:caslcompliance at wspgroup.com> caslcompliance at wspgroup.com so that we can promptly address your request. This message is intended only for the use of the individual or entity to which it is addressed, and may contain information which is privileged, confidential, proprietary or exempt from disclosure under applicable law. If you are not the intended recipient or the person responsible for delivering the message to the intended recipient, you are strictly prohibited from disclosing, distributing, copying or in any way using this message. If you have received this communication in error, please notify the sender, and destroy and delete any copies you may have received.
WSP provides professional land surveying services through the following entities: WSP Surveys (AB) Limited Partnership and WSP Surveys (BC) Limited Partnership
_____
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2014.0.4800 / Virus Database: 4311/9974 - Release Date: 06/08/15
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150611/45d6b097/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 6574 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150611/45d6b097/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 5585 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150611/45d6b097/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 7756 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150611/45d6b097/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 5918 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150611/45d6b097/attachment-0003.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 6538 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150611/45d6b097/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 30531 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150611/45d6b097/attachment.jpeg>
More information about the Equest-users
mailing list