[Equest-users] Fan usage - PTHP vs PSZ
Byron Burns
B.Burns at ha-inc.com
Mon Mar 16 08:04:39 PDT 2015
Hello Harshul,
I think it is because the PTAC interior fan is running intermittently where the PSZ is running continuous. You can check this quickly by changing the "indoor fan mode" of the PSZ from "Continuous" to "Intermittent". Even though you have selected the PTAC fan as "Constant Volume" the fan is cycling on and off to meet the space load, so if the hourly space load is 50% of the design load the fan will run for 30 minutes of the hour. The indoor fan mode is not editable for PTACs, but you may try setting it manually in the .inp file, I am not sure if it will work or not but would be worth a shot, just double check your hourly results.
[cid:image001.jpg at 01D05FD8.FF496880]
Byron D. Burns, EIT, BEMP
Energy Engineer, Building Sciences Studio
H&A | Hankins & Anderson | www.ha-inc.com<http://www.ha-inc.com>
d: (804) 420-1622 p: (804) 285-4171 f: (804) 217-8520
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Singhal, Harshul
Sent: Monday, March 16, 2015 10:20 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Fan usage - PTHP vs PSZ
Hello forum,
Our team received a note from our LEED reviewers that our equivalent full load hours (EFLH) in our baseline model were less than 8760, despite the ASHRAE 90.1 requirements that fans be run at constant speed 24 hours per day for multifamily occupancy type. Our baseline system type is PTHP. When we plot hourly fan energy usage for the building, usage varies hourly and loosely follows the profile of the outside air temperature. The EFLH is approximately 7517 hours (88%). When we switch the system to 'packaged single-zone heat pump' from 'packaged terminal heat pump' EFLH becomes 8760. This seems to indicate that the lower EFLH of our baseline model is somehow associated with the system type, however our team can't seem to figure out what characteristic of a PTHP causes fan energy to change hourly despite the 'constant speed' designation. Does anyone have any insight as to why PTHP EFLH would be below 8760 while packaged single-zone heat pump would not be? Thanks for any insight you might have.
Cheers,
[cid:image002.jpg at 01D05CF2.73106640]
Harshul Singhal, LEED AP BD+C
Project Consultant
Thornton Tomasetti
386 Fore Street, Suite 401
Portland, ME 04101
T +1.207.245.6060 F +1.207.245.6061
D +1.207.245.6074
HSinghal at ThorntonTomasetti.com<mailto:HSinghal at ThorntonTomasetti.com>
www.ThorntonTomasetti.com<http://www.ThorntonTomasetti.com>
<><><><><><><><><><><><><><><><><><><><><><><><><><><><><><><>
The information in this email and any attachments may contain
confidential information that is intended solely for the
attention and use of the named addressee(s). This message or
any part thereof must not be disclosed, copied, distributed
or retained by any person without authorization from the
addressee. If you are not the intended addressee, please
notify the sender immediately, and delete this message.
<><><><><><><><><><><><><><><><><><><><><><><><><><><><><><><>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150316/5f2be93a/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 99047 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150316/5f2be93a/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 50179 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150316/5f2be93a/attachment-0001.jpg>
More information about the Equest-users
mailing list