[Equest-users] Condensing boiler curve issues
Lapierre, Patrick
plapierre at bpa.ca
Tue Sep 22 13:38:15 PDT 2015
Hi Adam,
eQUEST's default curve performs just as you say it should.
Be careful that when you calculate your corrected efficiency, you must take the PLR into account.
The correct formula is :
Corrected Efficiency = Nominal Efficiency * PLR / f(PLR)
You calculate the f(PLR) with the eQUEST curve.
See below the quick graph I charted out :
[cid:image002.png at 01D0F555.125D3CF0]
CondBlr-HIR-fPLR&HWR
a
b
c
d
e
f
-0.09439243
0.90319633
0.01547839
0.00159793
-0.00000645
0.00111453
Nominal Efficiency
90%
PLR
Water T
f(PLR)
Corrected Efficiency
1
80
1.00000
90%
1
90
1.01616
89%
1
100
1.03103
87%
1
110
1.04461
86%
1
120
1.05690
85%
0.9
80
0.89782
90%
0.9
90
0.91287
89%
0.9
100
0.92662
87%
0.9
110
0.93909
86%
0.9
120
0.95026
85%
0.8
80
0.79596
90%
0.8
90
0.80989
89%
0.8
100
0.82253
88%
0.8
110
0.83388
86%
0.8
120
0.84394
85%
0.7
80
0.69440
91%
0.7
90
0.70721
89%
0.7
100
0.71874
88%
0.7
110
0.72898
86%
0.7
120
0.73792
85%
[cid:image003.jpg at 01D0F554.9B7098D0]
Patrick Lapierre_ing.
plapierre at bpa.ca
De : Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] De la part de Adam Barker
Envoyé : 22 septembre 2015 16:03
À : 'equest-users' <equest-users at lists.onebuilding.org>
Objet : [Equest-users] Condensing boiler curve issues
Has anyone come across issues with the default condensing boiler curve in eQuest? This curve is a function of part load and return water temperature, and based on how condensing boilers work you would anticipate the part load efficiency to get worse as return water temperature increased (assuming part load is the same).
I am seeing the opposite in eQuest, where the default 80F RWT is giving me a poor seasonal efficiency, and a temperature like 160 RWT (in the non-condensing spectrum) is giving me a very high seasonal efficiency.
Any insight into why this might be happening?
Adam Barker, MBSc, C.E.T., LEED AP BD+C
Energy Project Manager
Provident Energy Management Inc.
T: 416-736-0630 x 1874 | abarker at pemi.com<mailto:abarker at pemi.com>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150922/ebf316d3/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 1728 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150922/ebf316d3/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 30765 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150922/ebf316d3/attachment.png>
More information about the Equest-users
mailing list