[Hap-users] Simulating an exhaust fan to cool a transformer room
Dusko Nikolic
dulen at xtra.co.nz
Wed Aug 14 01:54:45 PDT 2013
I did that once using CAV DX unit.
I cant exactly remember because I don't have HAP in front of me but it
should go something like this:
1. you set up your room as usual. allow for some small quantity of
outdoor air in l/s
2. Set up DX CAV airhandler and choose supply air by quantity not
temperature. Use same amount of supply air as outdoor air in step 1
3. use direct exhaust from zone and set it up at same amount of air as
in step 1 and 2
4. use indoor temperature that you are targeting.
5. run hap and look at the coil load. If coil load is positive figure
increase air quantities in step 1, 2 and 3
6. run hap again and keep increasing air quantity until you get 0 for
coil load
And that should be it than.
Regards
On 13.08.2013 21:47, Matthew Scott wrote:
>
> Has anyone had any luck simulating the use of an exhaust fan drawing
> fresh air through a louver to cool a transformer room?
>
> Matt Scott
>
> N.E. Fisher & Associates, Inc.
>
> 329 East Second St, 2^nd Flr
>
> Boyertown, PA 19512
>
> e: mscott at nefisher.com
>
> p: 610-369-3190
>
> f: 610-369-3194
>
>
>
> _______________________________________________
> Hap-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/hap-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to HAP-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/hap-users-onebuilding.org/attachments/20130814/82210cac/attachment-0002.htm>
More information about the Hap-users
mailing list