[Trace-users] GSHPs in Trace 700

Dahlstrom, Aaron ADahlstrom at in-posse.com
Mon Sep 23 13:37:28 PDT 2013


Right on, thanks Eric.

Aaron Dahlstrom, PE, LEED(r) AP
In Posse - A subsidiary of AKF| 1500 Walnut Street, Suite 1414, Philadelphia, PA 19102
d: 215-282-6753| m: 267-507-5470| In Posse: 215-282-6800| AKF: 212-354-5656
e: ADahlstrom at in-posse.com | in posse web: www.in-posse.com<http://www.in-posse.com/> | akf web: www.AKFGroup.com

From: Sturm, Eric [mailto:esturm at trane.com]
Sent: Monday, September 23, 2013 4:33 PM
To: Dahlstrom, Aaron
Cc: Joe Chappell; 'trace-users at lists.onebuilding.org'
Subject: RE: GSHPs in Trace 700

Aaron,

To clear up any confusion, I'd like to comment on your statement on the usage of geothermal plants and TRACE 700 files.  TRACE is currently capable of modeling one geothermal field (as defined in the Geothermal Loop section of Plant Controls) per alternative.  Trane Customer Direct Services can help with modeling questions or capabilities questions.  The support center can be reached at 608-787-3926, option 1 or cdshelp at trane.com<mailto:cdshelp at trane.com>.

Thanks,
Eric Sturm
Applications Engineer
Trane Commercial Systems
Ingersoll Rand
3600 Pammel Creek Rd
La Crosse, WI 54601

Email:  esturm at trane.com<mailto:esturm at trane.com>
Website:  www.trane.com<http://www.trane.com>

From: trace-users-bounces at lists.onebuilding.org<mailto:trace-users-bounces at lists.onebuilding.org> [mailto:trace-users-bounces at lists.onebuilding.org] On Behalf Of Dahlstrom, Aaron
Sent: Monday, September 23, 2013 1:21 PM
To: Joe Chappell; 'trace-users at lists.onebuilding.org'
Subject: Re: [Trace-users] GSHPs in Trace 700

Joe -

The information I have heard (from this list serv, help files, and Trane Trace) has indicated that Trace can only model one geothermal plant per TRC file.

That said, I see nothing that would prohibit you from setting up multiple systems that all reference a common plant.

However, there will be a single "compressor" modeled.

Not sure if this is a LEED model - if so, per a recent LEED review we received, GBCI has requested us to -either- use the minimum EER / COP of all relevant heat pumps as the EER/COP entered into Trace, or to conduct averaging based on the ton-hours (eg capacity, quantity, hours of operation) of each system.

Aaron

Aaron Dahlstrom, PE, LEED(r) AP
In Posse - A subsidiary of AKF| 1500 Walnut Street, Suite 1414, Philadelphia, PA 19102
d: 215-282-6753| m: 267-507-5470| In Posse: 215-282-6800| AKF: 212-354-5656
e: ADahlstrom at in-posse.com<mailto:ADahlstrom at in-posse.com> | in posse web: www.in-posse.com<http://www.in-posse.com/> | akf web: www.AKFGroup.com

From: trace-users-bounces at lists.onebuilding.org<mailto:trace-users-bounces at lists.onebuilding.org> [mailto:trace-users-bounces at lists.onebuilding.org] On Behalf Of Joe Chappell
Sent: Monday, September 23, 2013 2:06 PM
To: 'trace-users at lists.onebuilding.org'
Subject: [Trace-users] GSHPs in Trace 700

Hello,

I am currently attempting to model several ground source heat pump systems on a single ground loop all in the same cooling plant.  Two of the ground source heat pumps have energy recovery and two do not.  In my analysis reports I am only seeing energy usage in "Cooling Equipment - Cooling Mode" for one of the four heat pumps.  Is Trace able to model this arrangement?  Any tips on how to handle would be greatly appreciated.

Joe


This e-mail may contain information that is confidential, privileged or otherwise protected from disclosure. If you are not an intended recipient of this e-mail, do not duplicate or redistribute it by any means. Please delete it and any attachments and notify the sender that you have received it in error. Unintended recipients are prohibited from taking action on the basis of information in this e-mail. E-mail messages may contain computer viruses or other defects, may not be accurately replicated on other systems, or may be intercepted, deleted or interfered without the knowledge of the sender or the intended recipient. If you are not comfortable with the risks associated with e-mail messages, you may decide not to use e-mail to communicate with In Posse.

________________________________

The information contained in this message is privileged and intended only for the recipients named. If the reader is not a representative of the intended recipient, any review, dissemination or copying of this message or the information it contains is prohibited. If you have received this message in error, please immediately notify the sender, and delete the original message and attachments.


This e-mail may contain information that is confidential, privileged or otherwise protected from disclosure. If you are not an intended recipient of this e-mail, do not duplicate or redistribute it by any means. Please delete it and any attachments and notify the sender that you have received it in error. Unintended recipients are prohibited from taking action on the basis of information in this e-mail. E-mail messages may contain computer viruses or other defects, may not be accurately replicated on other systems, or may be intercepted, deleted or interfered without the knowledge of the sender or the intended recipient. If you are not comfortable with the risks associated with e-mail messages, you may decide not to use e-mail to communicate with In Posse.

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20130923/7a5394fc/attachment-0002.htm>


More information about the Trace-users mailing list