[Trace-users] FW: GSHPs in Trace 700
Dahlstrom, Aaron
ADahlstrom at in-posse.com
Mon Sep 23 14:15:19 PDT 2013
Posting this back to the list as there may be other listeners who find it valuable.
Aaron Dahlstrom, PE, LEED(r) AP
In Posse - A subsidiary of AKF| 1500 Walnut Street, Suite 1414, Philadelphia, PA 19102
d: 215-282-6753| m: 267-507-5470| In Posse: 215-282-6800| AKF: 212-354-5656
e: ADahlstrom at in-posse.com | in posse web: www.in-posse.com<http://www.in-posse.com/> | akf web: www.AKFGroup.com
From: Joe Chappell [mailto:JoeC at designengineers.com]
Sent: Monday, September 23, 2013 5:16 PM
To: 'Sturm, Eric'; Dahlstrom, Aaron
Subject: RE: GSHPs in Trace 700
Thanks, Eric and Aaron, for all of the information and the prompt responses. I'm glad to have solid information to know the best possible approach to take with my configuration.
Joe
From: Sturm, Eric [mailto:esturm at trane.com]
Sent: Monday, September 23, 2013 4:11 PM
To: Dahlstrom, Aaron
Cc: Joe Chappell
Subject: RE: GSHPs in Trace 700
With geothermal loops, you'll have to use the weighted average approach or some other equivalent if required by an authoritative body.
Eric Sturm
Applications Engineer
Trane Commercial Systems
Ingersoll Rand
3600 Pammel Creek Rd
La Crosse, WI 54601
Office: +1.608.787.3736
Fax: +1.608.787.3005
Email: esturm at trane.com<mailto:esturm at trane.com>
Website: www.trane.com<http://www.trane.com>
From: Dahlstrom, Aaron [mailto:ADahlstrom at in-posse.com]
Sent: Monday, September 23, 2013 4:08 PM
To: Sturm, Eric
Cc: JoeC at designengineers.com<mailto:JoeC at designengineers.com>
Subject: RE: GSHPs in Trace 700
Great. I'm not familiar with plant sequencing so I appreciate your help.
So our best bet for a geothermal design with multiple styles (read EERs) of geothermal heat pumps is to input one cooling plant, one piece of equipment, and conduct a weighted average (by ton-hour) of the load handled by each distinct style, then enter that as a blended EER for our one piece of cooling equipment.
Aaron
Aaron Dahlstrom, PE, LEED(r) AP
In Posse - A subsidiary of AKF| 1500 Walnut Street, Suite 1414, Philadelphia, PA 19102
d: 215-282-6753| m: 267-507-5470| In Posse: 215-282-6800| AKF: 212-354-5656
e: ADahlstrom at in-posse.com<mailto:ADahlstrom at in-posse.com> | in posse web: www.in-posse.com<http://www.in-posse.com/> | akf web: www.AKFGroup.com
From: Sturm, Eric [mailto:esturm at trane.com]
Sent: Monday, September 23, 2013 5:06 PM
To: Dahlstrom, Aaron
Cc: JoeC at designengineers.com<mailto:JoeC at designengineers.com>
Subject: RE: GSHPs in Trace 700
Aaron,
You can do exactly what you want, if you're not simulating a geothermal field. You would have individual plants and assign the respective system coils to those plants. But, when you add a geothermal field into the mix, everything must be constrained to a single cooling plant.
I've been following this list since its inception and when I was program manager for TRACE 700. It's important that our users have accurate information.
Eric Sturm
Applications Engineer
Trane Commercial Systems
Ingersoll Rand
3600 Pammel Creek Rd
La Crosse, WI 54601
Office: +1.608.787.3736
Fax: +1.608.787.3005
Email: esturm at trane.com<mailto:esturm at trane.com>
Website: www.trane.com<http://www.trane.com>
From: Dahlstrom, Aaron [mailto:ADahlstrom at in-posse.com]
Sent: Monday, September 23, 2013 3:57 PM
To: Sturm, Eric
Cc: JoeC at designengineers.com<mailto:JoeC at designengineers.com>
Subject: RE: GSHPs in Trace 700
Again, helpful, Eric.
This directly applies to the other project I'm working through.
There is no sequencing that allows me to isolate the load from a specific system to a specific piece of cooling equipment, correct?
Ie what I'd like to do is have Heat Pump A with EER_A associated with thermal loads from System_A, and Heat Pump B with EER_B associated with thermal loads from System_B. I believe this is not possible.
Can you confirm?
Thank you!!! (glad you monitor this list.)
Aaron Dahlstrom, PE, LEED(r) AP
In Posse - A subsidiary of AKF| 1500 Walnut Street, Suite 1414, Philadelphia, PA 19102
d: 215-282-6753| m: 267-507-5470| In Posse: 215-282-6800| AKF: 212-354-5656
e: ADahlstrom at in-posse.com<mailto:ADahlstrom at in-posse.com> | in posse web: www.in-posse.com<http://www.in-posse.com/> | akf web: www.AKFGroup.com
From: Sturm, Eric [mailto:esturm at trane.com]
Sent: Monday, September 23, 2013 4:54 PM
To: Dahlstrom, Aaron
Cc: JoeC at designengineers.com<mailto:JoeC at designengineers.com>
Subject: RE: GSHPs in Trace 700
Aaron and Joe,
To be clear, you can only attach a single field and cooling plant together. But, you could have multiple pieces of equipment in a single cooling plant. This cooling plant could have a single geothermal field. It would look something like this on the Configuration screen:
[cid:image001.png at 01CEB878.2CC5A620]
You'd want to create each equipment type and assign a capacity and energy rate, and then adjust the sequencing. The trouble is, if you change the sequencing to parallel, each piece of equipment will load equally. You wouldn't see variation between pieces of equipment throughout the day because they will split the incoming coil loads.
Eric Sturm
Applications Engineer
Trane Commercial Systems
Ingersoll Rand
3600 Pammel Creek Rd
La Crosse, WI 54601
Email: esturm at trane.com<mailto:esturm at trane.com>
Website: www.trane.com<http://www.trane.com>
From: Dahlstrom, Aaron [mailto:ADahlstrom at in-posse.com]
Sent: Monday, September 23, 2013 3:41 PM
To: Dahlstrom, Aaron; Sturm, Eric
Cc: JoeC at designengineers.com<mailto:JoeC at designengineers.com>
Subject: RE: GSHPs in Trace 700
Eric - one followup question.
Is it possible to attach multiple cooling plants to the same field?
My understanding is no, but thought it worth it to confirm.
Aaron
Aaron Dahlstrom, PE, LEED(r) AP
In Posse - A subsidiary of AKF| 1500 Walnut Street, Suite 1414, Philadelphia, PA 19102
d: 215-282-6753| m: 267-507-5470| In Posse: 215-282-6800| AKF: 212-354-5656
e: ADahlstrom at in-posse.com<mailto:ADahlstrom at in-posse.com> | in posse web: www.in-posse.com<http://www.in-posse.com/> | akf web: www.AKFGroup.com
From: trace-users-bounces at lists.onebuilding.org<mailto:trace-users-bounces at lists.onebuilding.org> [mailto:trace-users-bounces at lists.onebuilding.org] On Behalf Of Dahlstrom, Aaron
Sent: Monday, September 23, 2013 4:37 PM
To: Sturm, Eric
Cc: 'trace-users at lists.onebuilding.org'
Subject: Re: [Trace-users] GSHPs in Trace 700
Right on, thanks Eric.
Aaron Dahlstrom, PE, LEED(r) AP
In Posse - A subsidiary of AKF| 1500 Walnut Street, Suite 1414, Philadelphia, PA 19102
d: 215-282-6753| m: 267-507-5470| In Posse: 215-282-6800| AKF: 212-354-5656
e: ADahlstrom at in-posse.com<mailto:ADahlstrom at in-posse.com> | in posse web: www.in-posse.com<http://www.in-posse.com/> | akf web: www.AKFGroup.com
From: Sturm, Eric [mailto:esturm at trane.com]
Sent: Monday, September 23, 2013 4:33 PM
To: Dahlstrom, Aaron
Cc: Joe Chappell; 'trace-users at lists.onebuilding.org'
Subject: RE: GSHPs in Trace 700
Aaron,
To clear up any confusion, I'd like to comment on your statement on the usage of geothermal plants and TRACE 700 files. TRACE is currently capable of modeling one geothermal field (as defined in the Geothermal Loop section of Plant Controls) per alternative. Trane Customer Direct Services can help with modeling questions or capabilities questions. The support center can be reached at 608-787-3926, option 1 or cdshelp at trane.com<mailto:cdshelp at trane.com>.
Thanks,
Eric Sturm
Applications Engineer
Trane Commercial Systems
Ingersoll Rand
3600 Pammel Creek Rd
La Crosse, WI 54601
Email: esturm at trane.com<mailto:esturm at trane.com>
Website: www.trane.com<http://www.trane.com>
From: trace-users-bounces at lists.onebuilding.org<mailto:trace-users-bounces at lists.onebuilding.org> [mailto:trace-users-bounces at lists.onebuilding.org] On Behalf Of Dahlstrom, Aaron
Sent: Monday, September 23, 2013 1:21 PM
To: Joe Chappell; 'trace-users at lists.onebuilding.org'
Subject: Re: [Trace-users] GSHPs in Trace 700
Joe -
The information I have heard (from this list serv, help files, and Trane Trace) has indicated that Trace can only model one geothermal plant per TRC file.
That said, I see nothing that would prohibit you from setting up multiple systems that all reference a common plant.
However, there will be a single "compressor" modeled.
Not sure if this is a LEED model - if so, per a recent LEED review we received, GBCI has requested us to -either- use the minimum EER / COP of all relevant heat pumps as the EER/COP entered into Trace, or to conduct averaging based on the ton-hours (eg capacity, quantity, hours of operation) of each system.
Aaron
Aaron Dahlstrom, PE, LEED(r) AP
In Posse - A subsidiary of AKF| 1500 Walnut Street, Suite 1414, Philadelphia, PA 19102
d: 215-282-6753| m: 267-507-5470| In Posse: 215-282-6800| AKF: 212-354-5656
e: ADahlstrom at in-posse.com<mailto:ADahlstrom at in-posse.com> | in posse web: www.in-posse.com<http://www.in-posse.com/> | akf web: www.AKFGroup.com
From: trace-users-bounces at lists.onebuilding.org<mailto:trace-users-bounces at lists.onebuilding.org> [mailto:trace-users-bounces at lists.onebuilding.org] On Behalf Of Joe Chappell
Sent: Monday, September 23, 2013 2:06 PM
To: 'trace-users at lists.onebuilding.org'
Subject: [Trace-users] GSHPs in Trace 700
Hello,
I am currently attempting to model several ground source heat pump systems on a single ground loop all in the same cooling plant. Two of the ground source heat pumps have energy recovery and two do not. In my analysis reports I am only seeing energy usage in "Cooling Equipment - Cooling Mode" for one of the four heat pumps. Is Trace able to model this arrangement? Any tips on how to handle would be greatly appreciated.
Joe
This e-mail may contain information that is confidential, privileged or otherwise protected from disclosure. If you are not an intended recipient of this e-mail, do not duplicate or redistribute it by any means. Please delete it and any attachments and notify the sender that you have received it in error. Unintended recipients are prohibited from taking action on the basis of information in this e-mail. E-mail messages may contain computer viruses or other defects, may not be accurately replicated on other systems, or may be intercepted, deleted or interfered without the knowledge of the sender or the intended recipient. If you are not comfortable with the risks associated with e-mail messages, you may decide not to use e-mail to communicate with In Posse.
________________________________
The information contained in this message is privileged and intended only for the recipients named. If the reader is not a representative of the intended recipient, any review, dissemination or copying of this message or the information it contains is prohibited. If you have received this message in error, please immediately notify the sender, and delete the original message and attachments.
This e-mail may contain information that is confidential, privileged or otherwise protected from disclosure. If you are not an intended recipient of this e-mail, do not duplicate or redistribute it by any means. Please delete it and any attachments and notify the sender that you have received it in error. Unintended recipients are prohibited from taking action on the basis of information in this e-mail. E-mail messages may contain computer viruses or other defects, may not be accurately replicated on other systems, or may be intercepted, deleted or interfered without the knowledge of the sender or the intended recipient. If you are not comfortable with the risks associated with e-mail messages, you may decide not to use e-mail to communicate with In Posse.
This e-mail may contain information that is confidential, privileged or otherwise protected from disclosure. If you are not an intended recipient of this e-mail, do not duplicate or redistribute it by any means. Please delete it and any attachments and notify the sender that you have received it in error. Unintended recipients are prohibited from taking action on the basis of information in this e-mail. E-mail messages may contain computer viruses or other defects, may not be accurately replicated on other systems, or may be intercepted, deleted or interfered without the knowledge of the sender or the intended recipient. If you are not comfortable with the risks associated with e-mail messages, you may decide not to use e-mail to communicate with In Posse.
________________________________
The information contained in this message is privileged and intended only for the recipients named. If the reader is not a representative of the intended recipient, any review, dissemination or copying of this message or the information it contains is prohibited. If you have received this message in error, please immediately notify the sender, and delete the original message and attachments.
This e-mail may contain information that is confidential, privileged or otherwise protected from disclosure. If you are not an intended recipient of this e-mail, do not duplicate or redistribute it by any means. Please delete it and any attachments and notify the sender that you have received it in error. Unintended recipients are prohibited from taking action on the basis of information in this e-mail. E-mail messages may contain computer viruses or other defects, may not be accurately replicated on other systems, or may be intercepted, deleted or interfered without the knowledge of the sender or the intended recipient. If you are not comfortable with the risks associated with e-mail messages, you may decide not to use e-mail to communicate with In Posse.
________________________________
The information contained in this message is privileged and intended only for the recipients named. If the reader is not a representative of the intended recipient, any review, dissemination or copying of this message or the information it contains is prohibited. If you have received this message in error, please immediately notify the sender, and delete the original message and attachments.
This e-mail may contain information that is confidential, privileged or otherwise protected from disclosure. If you are not an intended recipient of this e-mail, do not duplicate or redistribute it by any means. Please delete it and any attachments and notify the sender that you have received it in error. Unintended recipients are prohibited from taking action on the basis of information in this e-mail. E-mail messages may contain computer viruses or other defects, may not be accurately replicated on other systems, or may be intercepted, deleted or interfered without the knowledge of the sender or the intended recipient. If you are not comfortable with the risks associated with e-mail messages, you may decide not to use e-mail to communicate with In Posse.
________________________________
The information contained in this message is privileged and intended only for the recipients named. If the reader is not a representative of the intended recipient, any review, dissemination or copying of this message or the information it contains is prohibited. If you have received this message in error, please immediately notify the sender, and delete the original message and attachments.
This e-mail may contain information that is confidential, privileged or otherwise protected from disclosure. If you are not an intended recipient of this e-mail, do not duplicate or redistribute it by any means. Please delete it and any attachments and notify the sender that you have received it in error. Unintended recipients are prohibited from taking action on the basis of information in this e-mail. E-mail messages may contain computer viruses or other defects, may not be accurately replicated on other systems, or may be intercepted, deleted or interfered without the knowledge of the sender or the intended recipient. If you are not comfortable with the risks associated with e-mail messages, you may decide not to use e-mail to communicate with In Posse.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20130923/691567b2/attachment-0002.htm>