Set the z factor to a percentage such as 30 percent and those troublesome rooms like closets will automatically be over aired and control the AHU OA percentage. Use that feature quite often.
On Jun 5, 2014, at 2:05 PM, "Wohlgenant, Terry" <twohlgenant at DLRGROUP.com> wrote:
> I have used the same strategy. But raising the supply air volumes to the critical room above that required by your load simulation has the effect of raising the minimum air flow. That is what actually brings the percentage of OSA down. Raising the minimum stop on the VAV terminal unit that serves that room is probably the more correct way of handling this. Raising the minimum stop leads to re-heat to maintain room temperature which results in higher energy usage so watch your energy usage in your modeling runs and balance the re-heat need against higher OSA values. What will also help is to look at ASHRAE interpretation IC 62.1-2007-17. ASHRAE 62.1 does not require OSA in rooms that are not normally occupied.
>
>
> Terry L. Wohlgenant, CIPE, BEMP, LEED AP BD+C
> Mechanical Design | Senior Associate
> twohlgenant at dlrgroup.com
>
> DLR Group
> Architecture Engineering Planning Interiors
> o: 602-381-8580
> 6225 North 24th Street, Suite 250 Phoenix, AZ 85016-2042
> dlrgroup.com | listen.DESIGN.deliver
>
> dlrgroup.com is newly renovated and expanded. Click. Explore. http://www.dlrgroup.com
>
>
> -----Original Message-----
> From: Trace-users [mailto:trace-users-bounces at lists.onebuilding.org] On Behalf Of trace-users-request at lists.onebuilding.org
> Sent: Wednesday, June 04, 2014 1:06 PM
> To: trace-users at lists.onebuilding.org
> Subject: Trace-users Digest, Vol 66, Issue 1
>
> Send Trace-users mailing list submissions to
> trace-users at lists.onebuilding.org
>
> To subscribe or unsubscribe via the World Wide Web, visit
> http://lists.onebuilding.org/listinfo.cgi/trace-users-onebuilding.org
> or, via email, send a message with subject or body 'help' to
> trace-users-request at lists.onebuilding.org
>
> You can reach the person managing the list at
> trace-users-owner at lists.onebuilding.org
>
> When replying, please edit your Subject line so it is more specific than "Re: Contents of Trace-users digest..."
>
>
> Today's Topics:
>
> 1. Percent Outside Air (UNCLASSIFIED) (Eurek, John S NWO)
> 2. Re: Percent Outside Air (UNCLASSIFIED) (Scott Parker)
> 3. Re: Percent Outside Air (UNCLASSIFIED) (Michael Hardy)
> 4. REMINDER - onebuilding.org mailing lists (Jason Glazer)
>
>
> ----------------------------------------------------------------------
>
> Message: 1
> Date: Tue, 3 Jun 2014 20:16:01 +0000
> From: "Eurek, John S NWO" <John.S.Eurek at usace.army.mil>
> To: "trace-users at lists.onebuilding.org"
> <trace-users at lists.onebuilding.org>
> Subject: [Trace-users] Percent Outside Air (UNCLASSIFIED)
> Message-ID:
> <E777FD5A41D3B04A83296213737A85D7092E376C at EIS-MB0501WPC.eis.ds.usace.army.mil>
>
> Content-Type: text/plain; charset="us-ascii"
>
> Classification: UNCLASSIFIED
> Caveats: NONE
>
>
> I have an Variable Volume Reheat (30% Min Flow Default) and used the System Ventilation Flag to ASHRAE 62.1 with Vent Rest. When I ran the model the system was running 100% Outside air. I looked at the 62.1 report and saw that there were corridors and storage rooms driving the 100%, so I set the air flow for those rooms higher. I repeated this process of finding the critical zones and increasing the supply cfm to drive down the outside air percentage.
>
> I've got it down to 43.4%, but is there a better way to accomplish this?
>
> When I run it with summing outside air requirements, the highest zone is 32% outside air, but the values don't comply with 62.1.
>
> Is the best method just to find the critical zones and increasing the cfms and repeat?
>
>
>
> Classification: UNCLASSIFIED
> Caveats: NONE
>
>
>
>
> ------------------------------
>
> Message: 2
> Date: Tue, 3 Jun 2014 20:23:12 +0000
> From: Scott Parker <sparker at aeieng.com>
> To: "Eurek, John S NWO" <John.S.Eurek at usace.army.mil>,
> "trace-users at lists.onebuilding.org"
> <trace-users at lists.onebuilding.org>
> Subject: Re: [Trace-users] Percent Outside Air (UNCLASSIFIED)
> Message-ID: <6f376b91c33841e1a386a48256d00382 at MSN-EX2.aeieng.lan>
> Content-Type: text/plain; charset="us-ascii"
>
> I prefer manual calculations, but if you want to use Trace to do the ventilation calculations then you can set a "Max Vent (Z) Ratio Allowed". You can try a little trial and error but likely between 30 and 60%.
>
>
>
> [cid:image001.png at 01CF7F48.1C2BF750]
>
>
>
> SCOTT PARKER
>
>
>
> -----Original Message-----
> From: Trace-users [mailto:trace-users-bounces at lists.onebuilding.org] On Behalf Of Eurek, John S NWO
> Sent: Tuesday, June 03, 2014 4:16 PM
> To: trace-users at lists.onebuilding.org
> Subject: [Trace-users] Percent Outside Air (UNCLASSIFIED)
>
>
>
> Classification: UNCLASSIFIED
>
> Caveats: NONE
>
>
>
>
>
> I have an Variable Volume Reheat (30% Min Flow Default) and used the System Ventilation Flag to ASHRAE 62.1 with Vent Rest. When I ran the model the system was running 100% Outside air. I looked at the 62.1 report and saw that there were corridors and storage rooms driving the 100%, so I set the air flow for those rooms higher. I repeated this process of finding the critical zones and increasing the supply cfm to drive down the outside air percentage.
>
>
>
> I've got it down to 43.4%, but is there a better way to accomplish this?
>
>
>
> When I run it with summing outside air requirements, the highest zone is 32% outside air, but the values don't comply with 62.1.
>
>
>
> Is the best method just to find the critical zones and increasing the cfms and repeat?
>
>
>
>
>
>
>
> Classification: UNCLASSIFIED
>
> Caveats: NONE
>
>
>
>
>
> _______________________________________________
>
> Trace-users mailing list
>
> http://lists.onebuilding.org/listinfo.cgi/trace-users-onebuilding.org
>
> To unsubscribe from this mailing list send a blank message to TRACE-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:TRACE-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20140603/164aa4f5/attachment.html>
> -------------- next part --------------
> A non-text attachment was scrubbed...
> Name: image001.png
> Type: image/png
> Size: 38150 bytes
> Desc: image001.png
> URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20140603/164aa4f5/attachment-0001.png>
>
> ------------------------------
>
> Message: 3
> Date: Tue, 3 Jun 2014 13:24:48 -0700
> From: "Michael Hardy" <mhardy at blackoakengineering.com>
> To: "'Eurek, John S NWO'" <John.S.Eurek at usace.army.mil>,
> <trace-users at lists.onebuilding.org>
> Subject: Re: [Trace-users] Percent Outside Air (UNCLASSIFIED)
> Message-ID: <008001cf7f69$de9b3140$9bd193c0$@blackoakengineering.com>
> Content-Type: text/plain; charset="us-ascii"
>
> I usually delete the ventilation rates for those non-critical "critical"
> areas so they don't drive the minimum OSA settings. Janitor's closets are the worst, but then I use transfer air and exhaust for those which isn't modeled very well anyway.
>
> Michael L. Hardy, PE, F.NSPE
> Black Oak Engineering, Inc.
> Cell 503.314.5244
>
>
> -----Original Message-----
> From: Trace-users [mailto:trace-users-bounces at lists.onebuilding.org] On
> Behalf Of Eurek, John S NWO
> Sent: Tuesday, June 03, 2014 1:16 PM
> To: trace-users at lists.onebuilding.org
> Subject: [Trace-users] Percent Outside Air (UNCLASSIFIED)
>
> Classification: UNCLASSIFIED
> Caveats: NONE
>
>
> I have an Variable Volume Reheat (30% Min Flow Default) and used the System
> Ventilation Flag to ASHRAE 62.1 with Vent Rest. When I ran the model the
> system was running 100% Outside air. I looked at the 62.1 report and saw
> that there were corridors and storage rooms driving the 100%, so I set the
> air flow for those rooms higher. I repeated this process of finding the
> critical zones and increasing the supply cfm to drive down the outside air
> percentage.
>
> I've got it down to 43.4%, but is there a better way to accomplish this?
>
> When I run it with summing outside air requirements, the highest zone is 32%
> outside air, but the values don't comply with 62.1.
>
> Is the best method just to find the critical zones and increasing the cfms
> and repeat?
>
>
>
> Classification: UNCLASSIFIED
> Caveats: NONE
>
>
> _______________________________________________
> Trace-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/trace-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> TRACE-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
> ------------------------------
>
> Message: 4
> Date: Wed, 04 Jun 2014 15:03:00 -0500
> From: Jason Glazer <jglazer at gard.com>
> To: bldg-sim at onebuilding.org, equest-users at onebuilding.org,
> hap-users at onebuilding.org, trace-users at onebuilding.org,
> virtual-sim at onebuilding.org
> Subject: [Trace-users] REMINDER - onebuilding.org mailing lists
> Message-ID: <538F7B74.4060106 at gard.com>
> Content-Type: text/plain; charset=ISO-8859-1; format=flowed
>
> Posting Guidelines
> ------------------
>
> Please read the guidelines, especially if you want to post
> information about a product or an available job or if you
> want to post the same message to multiple lists.
>
> http://onebuilding.org/guidelines.html
>
> Share Your Answers
> ------------------
> If you are answering a question posted by someone else,
> please consider posting it to the list instead of privately
> answering. It is likely that others would be interested in
> the same question plus it makes both the question and the
> answer available in the archives.
>
> Cross Posting
> -------------
>
> If your question is specifically about eQUEST, HAP, or
> TRACE, IES-VE, please post your question to the
> eQUEST-users, HAP-users, TRACE-users or Virtual-Sim mailing
> lists first. If you haven't gotten an answer within a day or
> so, feel free to post the question to the BLDG-SIM mailing
> list.
>
> Other Mailing Lists
> -------------------
>
> To subscribe to the BLDG-SIM, eQUEST-users, HAP-users,
> TRACE-users or Virtual-Sim mailing lists, send a blank email to:
>
> bldg-sim-subscribe at onebuilding.org
> equest-users-subscribe at onebuilding.org
> hap-users-subscribe at onebuilding.org
> trace-users-subscribe at onebuilding.org
> virtual-sim-subscribe at onebuilding.org
>
> In addition we have a mailing list for building performance
> rating systems:
>
> bldg-rate-subscribe at onebuilding.org
>
> You can also subscribe to these lists from the
> onebuilding.org web site. In addition,links to mailing
> lists for some ASHRAE committees and USA chapter of IBPSA
> are available at the site.
>
> Unsubscribing
> -------------
>
> To unsubscribe, send a blank email to the appropriate email
> address shown below:
>
> bldg-sim-unsubscribe at onebuilding.org
> bldg-rate-unsubscribe at onebuilding.org
> equest-users-unsubscribe at onebuilding.org
> hap-users-unsubscribe at onebuilding.org
> trace-users-unsubscribe at onebuilding.org
> virtual-sim-unsubscribe at onebuilding.org
> 901ecb-unsubscribe at onebuilding.org
> 901env-unsubscribe at onebuilding.org
> 901fc-unsubscribe at onebuilding.org
> 901ltg-unsubscribe at onebuilding.org
> 901mech-unsubscribe at onebuilding.org
> spc140-l-unsubscribe at onebuilding.org
> tc47-l-unsubscribe at onebuilding.org
> tc28-l-unsubscribe at onebuilding.org
> ibpsausa-unsubscribe at onebuilding.org
>
> You can also unsubscribe on the onebuilding.org web site.
>
> Help, I Can't Post
> ------------------
>
> 90% of the time if you cannot post it is because you are
> sending from a different email address than the one you
> originally subscribed from. Please see "Changing Options"
> below to fix this. You can even change your email address
> for all of the mailing lists at once.
>
> Changing Options
> ----------------
>
> Go to the main web page
>
> http://onebuilding.org/
>
> Click on the link on the left for the mailing list you want
> to change your options on. At the bottom of the page for the
> specific mailing list, in the field near the button
> "unsubscribe or edit options" enter your email address and
> press that button. The next page will ask for a password, if
> you don't remember yours click on the remind button and one
> will be emailed to you. From this page you can change to
> digest mode or your email address or other options.
>
> Archives
> --------
>
> Each of the building energy simulation mailing lists have
> archives of the messages posted. There is a good chance you
> can find the answer you are looking for by searching the
> archives. Go to
>
> http://onebuilding.org/
>
> In each paragraph about the mailing list is a link to the
> archives. You can search that list from that page. In
> addition, you can use Google to search the entire site
> across all mailing lists by going to:
>
> http://onebuilding.org/search.html
>
> Digest Mode
> -----------
>
> If you would rather receive a single email each day with all
> of the messages within it, you can use Digest Mode. See the
> "Changing Options" section above to turn on Digest Mode.
>
> Links to Related Sites
> ----------------------
>
> If you are interested in other simulation program mailing
> lists or other sites related to building energy simulation,
> see the list of links at:
>
> http://onebuilding.org/links.html
>
> If you have suggestions for additional links, please send me
> an email.
>
> Subject Lines
> -------------
>
> For BLDG-SIM, if the question is about a specific simulation
> program, please include the name of the simulation program
> in the subject line. Also please post a question about a
> specific simulation program to the appropriate mailing list
> first to see if you can get an answer and post to BLDG-SIM
> the next day if you have not. If you are replying to a
> message in a digest, please see the section below.
>
> Replying to a Digest
> --------------------
>
> If you receive a digest, when replying to a message in the
> digest, please copy the original subject line and don't
> include the entire digest when replying. Just include the
> original message.
>
> I Still Need Help
> -----------------
>
> Please email me with your question, I'll try to help:
>
> jglazer at gard.com
>
> Suggestions
> -----------
>
> If you have suggestions on how to improve the mailing lists,
> add a mailing list, improve the onebuilding.org web site, or
> additions to this email message please send me an email.
>
> jglazer at gard.com
>
>
> --
> Jason Glazer, P.E., GARD Analytics, 90.1 ECB chair
> Admin for onebuilding.org building performance mailing lists
>
>
>
>
>
>
>
> ------------------------------
>
> Subject: Digest Footer
>
> _______________________________________________
> Trace-users mailing list
> Trace-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trace-users-onebuilding.org
>
>
> ------------------------------
>
> End of Trace-users Digest, Vol 66, Issue 1
> ******************************************
> _______________________________________________
> Trace-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/trace-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to TRACE-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
More information about the Trace-users
mailing list