Generally speaking I don't like to do it for a couple of reasons:
1. IMHO, it isn't practical. If people get hot, they are going to turn
on the air conditioning. If you don't allow them to, they are going to
complain to the point to where the building operator does it for them.
Your model should reflect that. If operable windows or an economizer is
available, however, then that is a different story.
2. Picking an arbitrary setpoint at which you "lockout" the cooling is
just that: arbitrary. At the very least, you should model your building
to determine its balance point and then use that point as your lockout
if you choose to use one at all. Even then, balance points change on a
zone-by-zone basis. You will want to refer to your unmet hours report to
make sure that any lockouts you apply to do not cause severe swings from
an acceptable setpoint.
3. Your model may include some rooms that have a high heat-gain, such as
computer rooms or perhaps rooms with equipment. (Copy machines,
printers, kitchen equipment such as refrigerators, etc.) This equipment
will release heat year-round, and could potentially mandate cooling for
either human comfort or proper equipment operation. Again, you can get
away with a cooling lockout if you have economizers or windows
available.
My experience with VRV is that most VRV airside units do not have
economizer capability. This, of course, depends on your project and job.
That you have cooling in the winter time doesn't necessarily raise a
red-flag to me. Many commercial buildings require some cooling in the
winter. You may want to dig into your outputs to figure out which zones
are asking for cooling and why. My assumption is that the lights,
occupancy, or equipment usage is creating a cooling load requiring
cooling. You may wish to review your lighting, occupancy, and equipment
schedules to ensure you feel they are accurate. Of course, internal
zones will require cooling before perimeter ones because they have a
higher skin loss.
Some points to consider, anyway.
Good luck!
-Gary
________________________________________________________________________
_______________________________________________
Gary Schrader | Schneider Electric | Buildings Business | Energy
Solutions | Engineer I
Phone: +1 | Mobile: +1 913 217 8068 | Fax: +1 913 469 0206
Email: gary.schrader at buildings.schneider-electric.com | Site:
www.schneider-electric.com/buildings | Address: 16011 College Boulevard,
Suite 212, Lenexa, KS 66219, USA
*** Please consider the environment before printing this email.
________________________________
From: Hind Dirani [mailto:hdirani at eegroup.info]
Sent: Friday, April 16, 2010 8:55 AM
To: Gary Schrader
Subject: RE: [Equest-users] eQuest Assistance
Gary,
I'm just referencing weather in the winter time as you said.
Is there a way to set all HVAC units in winter to heating mode only? Or
this idea isn't good
I'm very thankful; I will be waiting your response.
Hind
________________________________
From: Gary.Schrader at buildings.schneider-electric.com
[mailto:Gary.Schrader at buildings.schneider-electric.com]
Sent: Friday, April 16, 2010 3:17 PM
To: hdirani at eegroup.info
Subject: RE: [Equest-users] eQuest Assistance
Hind,
I'm not sure I'm following...
When you say there is no way to have cooling in the winter, are you
saying that you are configuring your system such that a cooling cycle
doesn't start below a certain outdoor temperature? Perhaps you are
configuring the system such that it only runs on certain calendar days?
Or, are you just referencing weather in the winter time as being too
cold to need cooling?
Thanks,
Gary
________________________________________________________________________
_______________________________________________
Gary Schrader | Schneider Electric | Buildings Business | Energy
Solutions | Engineer I
Phone: +1 | Mobile: +1 913 217 8068 | Fax: +1 913 469 0206
Email: gary.schrader at buildings.schneider-electric.com | Site:
www.schneider-electric.com/buildings | Address: 16011 College Boulevard,
Suite 212, Lenexa, KS 66219, USA
*** Please consider the environment before printing this email.
________________________________
From: Hind Dirani [mailto:hdirani at eegroup.info]
Sent: Thursday, April 15, 2010 9:42 AM
To: Gary Schrader
Subject: RE: [Equest-users] eQuest Assistance
Dear Gary
I took the liberty to directly email you and send you the .inp and .pd2
file as I don't seem to find a solution ( and I want to share my file)
Our project involves a VRV and our weather is based on Larnaka Cyprus
where there is no way to have space cooling in winter.
And in the simulation I got cooling in winter.
Can you help me to find the solution?
And, I just want to be sure of Cooling Electric input ratio in EQuest is
equal the inverse of COP?
IF it's not can you tell me the relation between them?
Any suggestion or help will be appreciated.
Thanks for your help
Hind
______________________________________________________________________
This email has been scanned by the MessageLabs Email Security System.
For more information please visit http://www.messagelabs.com/email
______________________________________________________________________
______________________________________________________________________
This email has been scanned by the MessageLabs Email Security System.
For more information please visit http://www.messagelabs.com/email
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100416/8bb14d87/attachment-0002.htm>
More information about the Equest-users
mailing list