[Equest-users] No Heating from PVVT Heat Pump
Eddie Corwin
ecorwin at altanova-energy.com
Wed Sep 29 13:35:14 PDT 2010
I will continue on with you suggestions. I is just hard for me to get past the
idea that when all of the HVAC systems are auto-sized, I still have many unmet
hours. If it were just a few unmet hours, I would be ok with it, but this
system has more than a few unmet hours.
The problem seems to be in the "WL/GS Ht Pump" input. There is no DOE2 help on
the topic, so it is hard to know exactly what is going on, but when it is set to
"NO" The HP runs in heating mode for ~1600 hours (with many unmet hours). When
the option is set to "YES" the heat pump runs for 3218 hours in heating mode
(with very few unmet hours). It seems that this option determines weather or
not the heat pump is able to operate at low outdoor temperatures,
or something along those lines. With the option set to "YES" I am still able to
have an air-cooled condenser, and I still have curves that relate the EIR and
capacity to the OA temperature. If you want to try this out, I have attached
the latest model.
Again, thank you for your suggestions, I always find it very helpful to have a
3rd party's comments
-Eddie
________________________________
From: "Bishop, Bill" <wbishop at pathfinder-ea.com>
To: Eddie Corwin <ecorwin at altanova-energy.com>
Cc: equest-users at lists.onebuilding.org
Sent: Wed, September 29, 2010 3:56:31 PM
Subject: RE: [Equest-users] No Heating from PVVT Heat Pump
Eddie,
You can see with your attached model that at least you are getting heating and
the system is operating. To get rid of your unmet hours, you will have to refine
the model. First put the accurate loads and envelope in (including getting rid
of the exterior floor I mentioned previously) and make sure your schedules
(lighting, equipment, occupancy etc.) are reasonable. Then change some interior
walls to air walls as applicable (interior walls that aren’t actually there,
such as corridors that open into a space without a door) to more evenly
distribute loads within each floor. Finally, add system capacities and zonal air
flows. Perimeter baseboard heating may be needed in the design if the windows
and walls are as poor as your previous attached model suggests. You might also
create a custom capacity curve (HEAT-CAP-FT) for the Mitsubishi heat pump.
Regards,
Bill
WilliamBishop , PE, BEMP, LEED® AP |Pathfinder Engineers & Architects LLP
Mechanical Engineer
134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005
wbishop at pathfinder-ea.com
www.pathfinder-ea.com
P Sustainability – the forest AND the trees.P
________________________________
From:equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Eddie Corwin
Sent: Wednesday, September 29, 2010 2:15 PM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] No Heating from PVVT Heat Pump
Bill and Kelly, thank you for your input.
Bill:
I have tried using the wizard to create the PVVT heat pump. I even used "system
per zone" so that each zone is controlled independently. Even coming strait out
of the wizard, there are plenty of heating hours not met. I understand that a
stand air-to-air heat pump will be unable to operate in very cold weather, but
that is where the supplemental heat should take over to get rid of any unmet
hours. I have attached this model.
The actual system I am trying to model is the Mitsubishi Hyper Heating Inverter
Y-Series Heat Pump. This system (in heating mode) uses electric resistance
heat to warm the outdoor air before it reaches the outdoor coils. This ensures
that heat transfer will occur between the OA and the outdoor coil, and allows
for operation at temperatures as low as -13*F. At first I thought that eQuest
can not exactly model a system like this, so maybe eQuest is not allowing any
heat transfer between the cold coil and the cold air. But then I tried again
using the RESVVT, and it seems to work well, even in the middle of winter. My
only objection to using the RESVVT is that I would like to have control over the
OA.
Kelly:
You say that I can not use PVVT with an air cooled compressor, but it says that
it is possible in the DOE2 help file, also, the wizard will set it up that way.
Normally I would just use the PSZ or even PTAC to model an air-to-air heat
pump, but I would like to use the variable speed compressor, so I need to use a
VVT system.
Has anyone modeled an air-to-air HP system that operates at such low
temperatures before?
Thanks,
-Eddie
________________________________
From:Dakota Kelley <dakotak at teliospc.com>
To: Eddie Corwin <ecorwin at altanova-energy.com>;
equest-users at lists.onebuilding.org
Sent: Wed, September 29, 2010 12:56:13 PM
Subject: RE: [Equest-users] No Heating from PVVT Heat Pump
Water-cooled heat pumps, ground loop or not, are considered system type PVVT.
Air-cooled heat pumps are considered type PSZ. Try changing your system type to
PSZ and your heating source to “heat pump”.
You can also create a temporary project and set up an air-source heat pump in
the wizard, then go inspect the system type/settings in the detailed interface
to see how eQUEST interprets your inputs.
Thanks,
DAKOTA KELLEY
Project Designer | Energy Analyst
Office: 214.744.6199
Cell: 214.280.3825
Fax: 214.744.0770
http://www.teliospc.com/ 3535 Travis St. Suite 115
dakotak at teliospc.com Dallas, TX
75204
| MEP ENGINEERING · ENERGY MODELING · LEED CONSULTATION · COMMISSIONING |
CONFIDENTIALITY NOTICE: This email is intended only for the use of the
individual or entity to which it is addressed,
And may contain information that is privileged, confidential and exempt from
disclosure under applicable law. If you
are not the intended recipient, please email the sender immediately, and delete
this email from all computers. Any
distribution or other use is strictly prohibited. Copyright © 2009 Telios
Corporation.
From:Eddie Corwin [mailto:ecorwin at altanova-energy.com]
Sent: Wednesday, September 29, 2010 8:43 AM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] No Heating from PVVT Heat Pump
So I determined why I was not getting any heating, and the resolutions perplexes
me.
I am modeling an Air-to-Air heat pump, so in the air-side system --> Basics tab
I selected "NO" for the field "WL/GS Ht Pump". In doing so, I get no heating
out of the system. When I change the field to "YES" I now get heating.
Attached are two images showing the field i am referring to, and
showing that I have an air-cooled condenser. Does anyone know why this might be
happening. I am worried that eQuest is treating my HP like a ground or
water source HP instead of an air-to-air system. Any thoughts on the matter
would be appreciated. By the way, I am using eQuest 3.64
-Eddie
________________________________
From:Eddie Corwin <ecorwin at altanova-energy.com>
To: equest-users at lists.onebuilding.org
Sent: Tue, September 28, 2010 5:17:21 PM
Subject: [Equest-users] No Heating from PVVT Heat Pump
I am trying to model a PVVT system, that uses an air-cooled heat pump for
heating and cooling. For some reason, the system refuses to supply any heating.
When I change the condenser type from air-cooled to water-cooled, the system
WILL provide heat. Has anyone experienced problems like this, or has
someone successful modeled a PVVT air-cooled heat pump? I have attached my IDF
and PD2 file for review.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100929/23ada9eb/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 2570 bytes
Desc: image002.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100929/23ada9eb/attachment-0001.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 286 Park Place.pd2
Type: application/octet-stream
Size: 54845 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100929/23ada9eb/attachment-0002.obj>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 286 Park Place.inp
Type: application/octet-stream
Size: 134797 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100929/23ada9eb/attachment-0003.obj>
More information about the Equest-users
mailing list