Thu Dec 1 05:47:56 PST 2011
Look thru the archives as this has been a previous issue for others. U probably need to input a reheat delta t in your system heating tab. Try a value of 30 to start.
Pashalu
Sent from my iPhone
On Nov 30, 2011, at 2:56 PM, Baran Tanrıverdi <tanriverdi.baran at gmail.com> wrote:
> Dear group members:
>
> A problem occured about heating load. I ve chosen both water coils for heating and cooling. After all when i run the simulation, thre is no heating load or any result about heating.
>
> Kind Regards.
>
> --
> Baran Tanrıverdi
>
>