[Bldg-sim] ASHRAE 90.1 "HC" heat capacity
Leonard Sciarra
leonard_sciarra at gensler.com
Thu Mar 25 08:12:56 PDT 2010
Seth, also Heat Capacities are listed for various blocks/block fill/concrete in Appendix A of 90.1.
Leonard Sciarra
Senior Associate
+1 (312) 577.6580 Direct
+1 (847) 345.5619 Cell
Gensler
11 East Madison Street
Suite 300
Chicago IL 60602
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Andy Hoover
Sent: Wednesday, March 24, 2010 8:34 PM
To: 'Seth P. Spangler'; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] ASHRAE 90.1 "HC" heat capacity
Hey Seth:
Check with the title 24 folk in CA. I believe they have/had tables and http://www.buildex.com/smartwall/tables/tpocmw.html buildex has some tables showing differing constructions HC.
Andy Hoover
Principal
The BEST Consultant, Inc.
Cell: 678-793-1159
Office: 678-200-7648
Fax: 678-827-0574
Email: andyhoover at thebestconsultant.com
Web: www.thebestconsultant.com
LEGAL DISCLAIMER
The information transmitted is intended solely for the individual or entity to which it is addressed and may contain confidential and/or privileged material. Any review, retransmission, dissemination or other use of or taking action in reliance upon this information by persons or entities other than the intended recipient is prohibited. If you have received this email in error please contact the sender and delete the material from any computer.
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Seth P. Spangler
Sent: Wednesday, March 24, 2010 9:44 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] ASHRAE 90.1 "HC" heat capacity
Hello,
ASHRAE defines a mass wall as a wall having a heat capacity (HC) of greater than 7 BTU/ft2 * F but I have been unable to find this property listed in tables of building materials. I am trying to calculate the heat capacity of a CMU wall and would like to confirm that my calculation methodology is correct.
Per ASHRAE 1997 Fundamentals:
* 8" concrete block - two cores filled with concrete (normal weight) - ~130 lb/ft3
* Thickness .67 ft
* Specific Heat ~ 0.22 BTU/lb * F
Therefore NC =(130 lb/ft3 )*(.67 ft)*(0.22 BTU/lb * F)
NC=19.16
Using this methodology even a 4" brick wall has a HC greater than 7 (7.5 to be exact).
Thanks in advance.
Seth Spangler, LEED(r) AP
Project Engineer
RMF Engineering, Inc
Ph: (843) 971-9639 ext:1497
Fax: (843) 971-9641
sspangle at rmf.com