[Bldg-sim] Process Loads
Nick Caton
ncaton at smithboucher.com
Fri Mar 18 13:57:45 PDT 2011
Assuming we're talking about 90.1, the definition for process load reads
something like "loads that don't have anything to do with HVAC..." so
you could make the case that a small IT closet split DX unit or
thermostat-controlled exhaust fan is not a process load, and therefore
the HVAC must be modeled as a system. Why would one want to do this?
You could demonstrate better performance with your efficient (?) system.
On the other hand, loads in small IT closest are commonly core zones
with 24/7 loads, and as a result any such system would be running 24/7
and/or on a consistent basis. An offshoot is you could very simply roll
any A/C for such spaces into the room's W/SF, and there would
potentially be little difference in consumed energy modeled. Why would
one want to do this? Objectively: It's easy/fast.
If those were the only two points of interest on the table, as your
reviewer I wouldn't care either way.
That said, the two above paths result in a pretty different baseline
scenario: On the one hand you end up with a baseline system against
which your proposed system may excel or underperform against in handling
the data/IT room's heat loads. In the other case you have zero direct
conditioning of the loads in that space in either model, which would
have to propagate into adjacent spaces/systems via partitions - which is
in most cases a step or two away from reality. Where one approach is
"removed" from reality and the other may objectively "reward/punish" the
design decisions made to condition that space, I think it's pretty clear
which is the preferable judgment from a reviewer's standpoint.
Then again, I'm not your reviewer ;).
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
Smith & Boucher Engineers
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
www.smithboucher.com
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Otto
Schwieterman
Sent: Friday, March 18, 2011 3:24 PM
To: Rob Hudson; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Process Loads
Rob,
You can try but I really doubt if the reviewer will see it that way. I
always consider it its own HVAC system in the proposed model and lump it
in with the one system per floor HVAC system in the baseline model.
I do not see much of a benefit for counting this as a process load,
maybe you can explain why you want to do this.
Otto
From: Rob Hudson [mailto:rdh4176 at gmail.com]
Sent: Friday, March 18, 2011 3:23 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Process Loads
I have a question about definition and correct interpretation. If I am
modeling building that has a space with a data rack and its own cooling
system separate from the rest of the buildings systems, is the cooling
considered process energy because it is "required" to be there similar
to the data rack electrical energy?
thanks in advanced,
--
Rob Hudson
________________________________________________________________________
________________
Fanning/Howey Associates, Inc. intends to send this transmission
(including any attachments) only to the
designated individual or entity. If you received this message in
error, please notify the sender by replying
to the electronic mail (if electronic) or by telephone at the number
indicated on this document.
Fanning/Howey Associates, Inc. has taken reasonable precautions to
ensure no viruses are present in the
electronic mail. Fanning/Howey Associates, Inc., will not accept
responsibility for any loss or damage arising
from the use of this electronic mail or attachments. Use, disclosure,
dissemination, distribution, or reproduction
of this message by unintended recipients is not authorized and maybe
unlawful. Any information included in
this transmission that is not related to contracts with our
authorization, verbal or written, by Fanning/Howey
Associates, Inc. may not be covered by our professional liability
insurance.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110318/ff8d7179/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110318/ff8d7179/attachment-0002.jpeg>
More information about the Bldg-sim
mailing list