Steven---
USGBC released a document titled "Treatment of District or Campus
Thermal Energy in LEED v2 and LEED 2009 - Design & Construction" in
August of 2010. This has all of the guidance you'll need for creating
a baseline and proposed design energy model for your project (it's not
that fun). There are two options to show compliance, the first being a
building stand-alone scenario (most popular I'm guessing) and the second
an aggregate building/DES scenario. Both of your baseline and proposed
models would utilized purchased steam and chilled water per page 11 of
the guidelines. Here is a link to the guidelines:
http://www.usgbc.org/ShowFile.aspx?DocumentID=7671
Good luck with the simulation.
Regards,
Andrew Craig PE, LEED AP
Project Mechanical Engineer
INTERFACE ENGINEERING
708 SW Third Avenue, Suite 400, Portland, OR 97204
email andrewc at interfaceeng.com <mailto:andrewc at interfaceeng.com>
portland 503.382.2696
www.interfaceeng.com <http://www.interfaceeng.com/>
Portland / Sacramento / San Francisco / Seattle
Celebrating 100 LEED Projects!
<http://interfaceengineering.com/sustainable-engineering/>
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Steven
Savich
Sent: Tuesday, October 09, 2012 4:15 PM
To: bldg-sim at lists.onebuilding.org
Cc: equest-users at lists.onebuilding.org
Subject: [Bldg-sim] LEED NCv2009 - baseline for gymnasium
All,
I'm at the planning stage for a LEED NC v 2009 compliance model. The
building is a university gymnasium with a main gym and two practice
gyms. The facility also contains locker rooms, a weight room, a sports
medicine area, offices, classrooms, and circulation spaces. The
building has two floors above grade, plus a basement mechanical room,
with a floor area of roughly 90,000 SF. Most of the facility is
gymnasium space, the other ("non-predominant") uses do not individually
total over 20,000SF in area. The heating source is a campus steam loop
fed by a central plant with natural gas-fired steam boilers. Cooling is
by a campus chilled water loop. Based on G3.1.1 and table G3.1.1A, the
required LEED baseline HVAC system will be System 5-Packaged VAV with
Reheat - DX cooling and Hot-water fossil fuel boiler.
My read on this is that, for the LEED baseline, I will have two separate
system 5's, one for each floor, with a unit heater for the basement mech
room. Since the campus has central heating and cooling, do I use those
systems to provide heating & cooling sources for the LEED baseline, or
do I use DX cooling and a hot water fossil fuel boiler per table
G3.1.1B?
Thanks in advance.
Steven
Steven Savich, LEED AP
Systems West Engineers
411 High Street
Eugene, OR 97401-2427
(541) 342-7210
(541) 342-7220 (fax)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20121009/54975281/attachment-0002.htm>
More information about the Bldg-sim
mailing list