[Bldg-sim] Regarding problem of Zero Electric Demand
Nick Caton
ncaton at smithboucher.com
Tue Nov 12 07:39:07 PST 2013
Best bet for eQuest-specific help is usually the [Equest-users] archives and the mailing list community, and there's an E+ counterpart mailing list as well. That said a substantial amount of eQuest-specific and E+-specific queries are handled here as well on [Bldg-sim] - sometimes it's not always clear when a question is specific to software or more general in nature so the the [bldg-sim] serves as an effective catch-all.
To Tom's eQuest query (and I'm speaking specifically to eQuest - E+ users will have to confirm if any of this applies on your end):
It's important to recognize that monthly and annual "peak demand" values reported in most detailed/graphical reports do not strictly represent the maximum draw of each end-use - they represent the hour with the maximum draw on the associated meter, broken out by end-use through that hour.
By extension, your cooling system(s) can be operating normally and keeping the spaces cool when called for, but not be operating within the hour of maximum draw for each month or for the year. This is not uncommon in the winter months for temperate and heating-dominated climates, particularly when there's substantial electric heating in play to overwhelm what the cooling systems require.
So that said, the graphical "Annual peak demand by end use" report is if I'm not mistaken reporting enduse draws for the peak hour over the whole simulated year - not seeing cooling in this pie chart is simply indicative of more substantial heating operating under the same meter. You can review and confirm if and when cooling plays a part in your monthly peak demands by reviewing the monthly graphical charts or via the PS-E/PS-F detailed reports.
Regards,
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Jim Dirkes
Sent: Tuesday, November 12, 2013 7:48 AM
To: Tom Mickley; Sheelam Khare; Bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Regarding problem of Zero Electric Demand
You have already decided that it is impossible for a working HVAC and lighting system to have zero demand. Have you confirmed that these systems are actually operating? i.e., is there energy consumption? If not, check schedules to make sure the systems turn on or (for HVAC) check setpoints to confirm that there is a demand.
If energy is consumed, but demand is not shown, you probably want to send the file to the E+ Help Desk. (I'm not sure how eQuest users get help :()
James V Dirkes II, PE, BEMP, LEED AP
www.buildingperformanceteam.com<http://www.buildingperformanceteam.com/>
Energy Analysis, Commissioning & Training Services
1631 Acacia Drive, Grand Rapids, MI 49504 USA
616 450 8653
From: bldg-sim-bounces at lists.onebuilding.org<mailto:bldg-sim-bounces at lists.onebuilding.org> [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Tom Mickley
Sent: Tuesday, November 12, 2013 8:15 AM
To: Sheelam Khare; Bldg-sim at lists.onebuilding.org<mailto:Bldg-sim at lists.onebuilding.org>
Subject: Re: [Bldg-sim] Regarding problem of Zero Electric Demand
I am also having a similar problem for an office building in Ohio using eQuest. The annual peak demand by end use report shows zero demand for cooling, yet there is the expected amount of space cooling in the monthly peak demand by end use and the expected amount of space cooling consumption kWh usage. Everything else seems to be in order....
Could this be an eQuest glitch?
Thanks,
Tom Mickley
Mechanical Engineer CEM
From: bldg-sim-bounces at lists.onebuilding.org<mailto:bldg-sim-bounces at lists.onebuilding.org> [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Sheelam Khare
Sent: Tuesday, November 12, 2013 12:24 AM
To: Bldg-sim at lists.onebuilding.org<mailto:Bldg-sim at lists.onebuilding.org>
Subject: [Bldg-sim] Regarding problem of Zero Electric Demand
Hello All,
I am using Energy Plus software to analyse a building located in Barcelona, Spain. In the LEED report it is indicating the Electric Demand for space cooling & Interior Lighting is zero, is it possible?
I have tried many times to solve this but unable to do so, please suggest me how can i resolve this problem?
Thanks with regards
Sheelam Khare
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20131112/85745cb3/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20131112/85745cb3/attachment-0002.jpg>
More information about the Bldg-sim
mailing list