[Bldg-sim] Regarding problem of Zero Electric Demand
Justin Spencer
jspencer17 at gmail.com
Tue Nov 12 08:18:24 PST 2013
Have you all looked at your hourly output to see what's going on there?
That always seems like a prudent first step in model debugging. I look at
hourly output from all models. That gets you closer to the root of the
problem, rather than looking at a particular report that you might or might
not understand.
On Tue, Nov 12, 2013 at 6:47 AM, Jim Dirkes <jim at buildingperformanceteam.com
> wrote:
> You have already decided that it is impossible for a working HVAC and
> lighting system to have zero demand. Have you confirmed that these systems
> are actually operating? i.e., is there energy consumption? If not, check
> schedules to make sure the systems turn on or (for HVAC) check setpoints to
> confirm that there is a demand.
>
> If energy is consumed, but demand is not shown, you probably want to send
> the file to the E+ Help Desk. (I’m not sure how eQuest users get help L)
>
>
>
> *James V Dirkes II, PE, BEMP, LEED AP*
> *www.buildingperformanceteam.com*<http://www.buildingperformanceteam.com/>
> *Energy Analysis, Commissioning & Training Services*
> 1631 Acacia Drive, Grand Rapids, MI 49504 USA
> 616 450 8653
>
>
>
> *From:* bldg-sim-bounces at lists.onebuilding.org [mailto:
> bldg-sim-bounces at lists.onebuilding.org] *On Behalf Of *Tom Mickley
> *Sent:* Tuesday, November 12, 2013 8:15 AM
> *To:* Sheelam Khare; Bldg-sim at lists.onebuilding.org
> *Subject:* Re: [Bldg-sim] Regarding problem of Zero Electric Demand
>
>
>
> I am also having a similar problem for an office building in Ohio using
> eQuest. The annual peak demand by end use report shows zero demand for
> cooling, yet there is the expected amount of space cooling in the monthly
> peak demand by end use and the expected amount of space cooling consumption
> kWh usage. Everything else seems to be in order….
>
>
>
> Could this be an eQuest glitch?
>
>
>
> Thanks,
>
>
>
> Tom Mickley
>
> Mechanical Engineer CEM
>
>
>
>
>
> *From:* bldg-sim-bounces at lists.onebuilding.org [
> mailto:bldg-sim-bounces at lists.onebuilding.org<bldg-sim-bounces at lists.onebuilding.org>]
> *On Behalf Of *Sheelam Khare
> *Sent:* Tuesday, November 12, 2013 12:24 AM
> *To:* Bldg-sim at lists.onebuilding.org
> *Subject:* [Bldg-sim] Regarding problem of Zero Electric Demand
>
>
>
> Hello All,
>
> I am using Energy Plus software to analyse a building located in
> Barcelona, Spain. In the LEED report it is indicating the Electric Demand
> for space cooling & Interior Lighting is zero, is it possible?
>
> I have tried many times to solve this but unable to do so, please suggest
> me how can i resolve this problem?
>
>
>
> Thanks with regards
>
> Sheelam Khare
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20131112/45c7688e/attachment-0002.htm>
More information about the Bldg-sim
mailing list