Thanks Jeff and John.  Yes, the building azimuth is north-south (actually
180 deg).  The space azimuth is 0 deg.  Only the wall is 1.27 deg off
straight east.  
"East"  should be anything between 67.5 and 112.5 deg.  
 
Shaun
 
From: Jeff Haberl [mailto:jhaberl at tamu.edu] 
Sent: Tuesday, July 08, 2014 3:10 PM
To: John Aulbach; Shaun Martin; bldg-sim at lists.onebuilding.org
Subject: RE: [Bldg-sim] Azimuth in equest
 
 
 
 Shaun,
 
Also, within DOE-2 simulations there are (3) orientations: the building, the
space and the exterior/interior surface. Hence, you can easily have a -91.27
= northeast if you don't know all (3) orientations. You can see this in the
LV- or verification reports for LOADS. You should be able to see this in the
"viewer" as well (of which there are several).
 
Jeff
 
8=!  8=)  :=)  8=)  ;=)  8=)  8=(  8=)  8=()  8=)  8=|  8=)  :=')  8=) 8=?
Jeff S. Haberl, Ph.D.,P.E.inactive,FASHRAE,FIBPSA,......jhaberl at tamu.edu
<mailto:........jhaberl at tamu.edu> 
Professor...................................................................
.....Office Ph: 979-845-6507
Department of Architecture............................................Lab
Ph:979-845-6065
Energy Systems Laboratory...........................................FAX:
979-862-2457
Texas A&M
University...................................................77843-3581
College Station, Texas, USA,
77843..............................URL:www.esl.tamu.edu
8=/  8=)  :=)  8=)  ;=)  8=)  8=()  8=)  :=)  8=)  8=!  8=)  8=? 8=) 8=0
  _____  
From: Bldg-sim [bldg-sim-bounces at lists.onebuilding.org] on behalf of John
Aulbach [jra_sac at yahoo.com]
Sent: Tuesday, July 08, 2014 4:53 PM
To: Shaun Martin; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Azimuth in equest
I am going to guess your Ploygon is part of a larger building. When you say
you set the Azimuth of the Polygon, what is the Azimuth of the Building
itself?
 
John R. Aulbach, PE 
 
On Tuesday, July 8, 2014 10:41 AM, Shaun Martin
<smartin at shaunmartinconsulting.com> wrote:
 
In equest, SHAPE = POLYGON  determines the x, y, z, azimuth.  Does anybody
happen know why a wall with an azimuth of -91.27 deg would be listed as
NORTH-EAST in the LV-D report?  Is there any easy way to fix this without
redoing all the polygons?  (Specifying the AZIMUTH does not work.)
 
Thanks,
 
Shaun Martin LEED AP
Principal
Shaun Martin Consulting
2060 Pine Street
Vancouver, BC V6J 4P8
P: 604-789-1095
E: smartin at shaunmartinconsulting.com
 
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send  a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20140708/71c0393e/attachment.htm>
    
    
More information about the Bldg-sim
mailing list