Re: [EnergyPlus_Support] zone axis



Lourenço:

EnergyPlus ignores wall thickness.  Surfaces are a plane with no 
thickness.  Since surface heat transfer is 1-dimensional in 
EnergyPlus, some modelers choose to use center lines for all walls so 
that the surface area is the average of the inside and outside 
surface areas.  For most typical walls, the impact on results for 
outside, centerline, or inside dimensions will be quite small.  So, 
in general, you may use whichever dimenstion is most easily obtained.

Many users ask if the surfaces must meet to form a complete enclosure 
with no gaps.  For heat transfer purposes, gaps between surfaces do 
nothing, only the surfaces transfer heat.  But if you are using Solar 
Distribution=FullInteriorAndExterior (in the Building object) or 
daylighting with reference points, then all zones must be convex 
enclosures with no gaps in order to determine the distribution of 
solar energy entering the space.

Mike Witte



On 5 Apr 2002, at 11:16, nuno lourenço wrote:

> I have doubts were is the best "location" to put the zoe axis.
> For the drawing in the PDF file where is the best location for zone 9 
> axis?My choice was the dot in the left corner.
> I also have doubts for zone 10 and 11.
> If anyone give me their opinion I thanks.
> Assume wall´s thickness and other measures.
> I want to know where do you put the zone axis for zone 9,10,11.
> And also the coordinates for one exterior wall and one interzone wall.
> How does wall thickness "works" in energyPlus?
> 
> Lourenço
> 
> _________________________________________________________________
> Chegou o novo MSN Explorer. Instale já. É gratuito: 
> http://explorer.msn.com.br
> 
> 
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> 
> 
> 
>  
> 
> Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/ 
> 
> 



========================================================
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx


------------------------ Yahoo! Groups Sponsor ---------------------~-->
SALE --> Wireless Video Cameras
for Home Surveillance! VERY TINY! PRICE BREAKTHROUGH - $79.99!
http://us.click.yahoo.com/W0toNC/7o6DAA/yigFAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/