Re: [EnergyPlus_Support] exterior window
At 04:00 AM 4/19/02, you wrote:
I have
windows in the exterior layer.They start at the floor of level zero and
go to the roof of the last level.
How can I model this situation?I have to define
the geometry of the wall in SURFACE:HEAT TRANSFER and then go to
WindowFrameAndDivider to model the window giving the same coordinates of
the wall?? IF so, I don`t have to give the information of the
construction layers (it`s the window) ???
Not quite.
As you say, the Surface:HeatTransfer models the wall. To be
expedient, use a construction with just an R value.
Then, you put in the Window with the Surface:HeatTransfer:Sub and put in
almost the same coordinates as the wall but leave just a very small
amount that will be the wall.
Then, you can add frames or dividers if you have them.
Linda