On 18 Jul 2002, at 12:07, habaza11@xxxxxx wrote:
> Thank you;
> I am trying to predict the surface temperature to a concrate ramp
That is an interesting problem. One approach would be to model the
ramp as the roof of a zone (the zone would not need any other
surfaces. Use purchased air to control the zone to your best
estimate of the soil temperature at 1 to 2 ft below the surface.
Then describe the roof construction as concrete plus 1 to 2 ft of
soil. The roof exterior surface temperature would be the ramp
surface temperature.
Since there are many unknowns here, you should test the sensitivity
of the result by altering the zone temperature over a reasonable
range and altering the soil conductivity. Be sure to specify OUTSIDE
CONVECTION ALGORITHM, Detailed;
Mike
> "Michael J. Witte" <mjwitte@xxxxxxxx> wrote:
>
> >In EnergyPlus, the inside of every surface is assumed to be in
> >contact with the zone air. What are you trying to model?
> >
> >Mike
> >
> >
> >On 18 Jul 2002, at 10:35, habaza11@xxxxxx wrote:
> >
> >> Hi; Is it possible to simulate a floor in E+ that its outside face
> >> faces the exterior invironment and its inside surface face the
> >> ground? Thank you in advance.
> >>
> >
> >
> >========================================================
> >EnergyPlus Testing and Support
> >EnergyPlus-Support@xxxxxxxx
> >
> >
> >
> >To unsubscribe from this group, send an email to:
> >EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> >
> >The primary EnergyPlus web site is found at:
> >http://www.energyplus.gov
> >
> >The group web site is:
> >http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> >
> >
> >
> >
> >
> >Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/
> >
> >
> >
>
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
>
>
>
>
>
> Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/
>
>
========================================================
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Will You Find True Love?
Will You Meet the One?
Free Love Reading by phone!
http://us.click.yahoo.com/ps3dMC/R_ZEAA/Ey.GAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/