Re: [EnergyPlus_Support] heating and cooling setpoints
I do not believe that the loads convergence issues would be causing
these problems. If you wish to always maintain the temperature
between 20 and 23C, then use must use the Dual Setpoints option. If
you use single setpoints, then you must schedule when the system is
in heating mode or cooling mode. With single setpoins, the zone
could get warmer than 23C if the weather gets warm when the single
heating setpoint control is active, or the zone could get colder than
20C with cold weather when the cooling control is active. The only
way to automatically switch between cooling and heating as needed
with a deadband in betwee is to use the DUAL SETPOINT WITH DEADBAND
control type.
Mike
On 15 Nov 2002, at 15:14, nuno lourenço wrote:
>
>
> I want to apologise because I found another error in my file.
> How could I want the setpoints to work (I want to maintain a
> temperature between 20-23) if I choose Single Heating and Single
> Heating instead of Dual Setpoint??? I am not using all my brain.I am
> runnig the file now to check the heating and cooling loads. I read in
> previous e-mail that there is a problem with load convergence criteria
> in heating/cooling loads. I was obtaining high loads in certain hours
> in the previous file I send.Could this be because of that?Maybe with
> the correction of setpoints the loads decrease.
>
> Best regards
>
> Lourenço
>
========================================================
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/